    General Electric Type U Transformer Bushing

    Thanks, Pete, I saw that earlier and after digging all day, I may just replace them. Chad Snyder
  2. Chad12

    General Electric Type U Transformer Bushing

    Hello, all! I am wondering if anyone has any info on GE type U bushings (Cat# 11B575BB G7) I have 3 of them (from 1971 but unused). They were stored horizontally for 40 years and I am hoping to find a drawing or other literature. Thanks! Chad
  3. Chad12

    Substation Ground Test

    An interesting item.... I was handed some papers regarding ground testing for an existing peak generating facility. One set of documents was a test using the slope method, no problem. The other document is something I have never seen before and I can't find anything in IEEE about it. It gives...
  4. Chad12

    Switchgear Failure Vacuum Bottle & Arresters

    Hello all, I have another interesting event to pass along.. Recently I was testing a 15KV Cable (EPR 133% insulation). This cable was a combination of old and new cables spliced together and terminated at several switches, with a total length of about 5,000 feet. The customer requested a test...
  5. Chad12

    Retrofit Trip unit for 600 V breaker and arc Flash

    The AC pro is a good option but I would keep in mind the pitiful reputation (well deserved) that FPE breakers have. I would recommend an aggressive maintenance/inspection interval for this equipment as mechanical operating time for this breaker is not improved by any trip unit. ABB makes a...
  6. Chad12

    Help with 15KV Switchgear

    Hello all, I have a question regarding 15KV metal-clad switchgear. The facility I am at this week is using ABB 15KV switchgear and supplying it with a nominal voltage of 16,600 volts. I cannot find anything in IEEE that addresses justification for using this voltage on 15KV gear. Any help would...
  7. Chad12

    Grounding balls into 34.5 kv switchgear

    I am a "by the book" power system service manager. I do not have an opinion on the proper way to perform electrical work, I follow established procedures and standards. I recently began a project, installing grounding balls into 34.5 kv switchgear to make grounding easier. I did the first three...
  8. Chad12

    check electrical safety in a plant

    Are you talking about periodic maintenance on electrical equipment? Chad Snyder Director of Operations American Power Technology http://www.ampowertech.com
  9. Chad12

    Motoring Generator by Breaker Failure

    waross, are you referring to an undervoltage trip coil? Chad Snyder Director of Operations American Power Technology http://www.ampowertech.com
  10. Chad12

    Transformer Excitation Test.

    A very simple way to accomplish this is to use a Megger brand digital 3 phase TTR. The turns ratio test, of course must be performed anyway, and this unit also displays excitation current data at the same time. 2 birds, 1 stone. Chad Snyder Director of Operations American Power Technology...
  11. Chad12

    Insuation Resistance Problem on Generator Stator

    I agree that all connections must be isolated to perform this test, yes humidity is a big factor, and there is also a temperature correction factor that must be applied. Chad Snyder Director of Operations American Power Technology http://www.ampowertech.com
  12. Chad12

    transformer protection: which relay trips which circuit breakers?

    A good reference would be one of the most common electromechanical relays around. It is the IAC relay from GE. Figure 7A on page 7 of this PDF shows an operating curve for the instantaneous function. Keep in mind that total operating time for the circuit includes mechanical operating time of the...