    3 thoughts 1) If your using 2 different manufacturers to supervise weak engineering, update your engineers. 2) We have never paid for a Schweitzer repair in 15yrs. They have warrantied everything so far... 3) Tech/engineering support for SEL relays is second to NONE! Cheers Chris
  2. Ceast

    MOLDED case breaker commissioning

    Step one download the manual for your breaker & trip unit. Step 2 read the attached...
  3. Ceast

    India - 370M INDIANS SWELTER IN HEAT AFTER POWER FAILS

    Some speculation that India drank the coal plant de-commissioning Koolaid. Only spectulation at this point.
  4. Ceast

    multin 489 protection relay

    Test the enabled elements with a Doble 6150.
  5. Ceast

    Fully automated testing

    Go here http://enoserv.com/ENOSERV-RTS-relay-testing-software.html
  6. Ceast

    unusual LTC DGA results

    Test contact resistance. When was the last time the LTC was opened up and inspected or repaired?
  7. Ceast

    unusual LTC DGA results

    See the attachment. http://files.engineering.com/getfile.aspx?folder=1db56989-0652-4e4a-ae92-fe3e5ddac91d&file=2005-LTC_Diagnostics.pdf
  8. Ceast

    Germany closes all nuclear plants.

    I think the Germans are going to import more French nuclear power and burn wood. Scotty you're half correct "Never underestimte the stupidity of politicians" Never underestimate the stupidity of the voting public.
  9. Ceast

    Neutrals on grid connected generators

    There are wye generators connected to a wye / delta GSU?
  10. Ceast

    Neutrals on grid connected generators

    What is your total N current as a % of full load? If the units are paralleled to the grid they sould be fine running in PF mode. What type of regulators? Is there a droop CT input? Have you tried running your 600kw paralleled with the 2nd unit off?
  11. Ceast

    remote radiator affecting turbocharged diesel genset?

    You could always measure the delta T across the aftercooler circuit.
  12. Ceast

    GSU transformer unique PF tests

    Doesn't look right. Not enough detail though. Totally isolated bushings? Everyting de-termed? Testset type? Humidity? Oil sample?
  13. Ceast

    Suitable replacement for a Caterpillar DVR

    Yep VR6 is the bomb and inexpensive. A little droop is a good thing.
  14. Ceast

    RE: Busbar Insulation Resistance Testing

    Precisely why we commisson equipment, gathering baseline data with temp correction and himidity recordings. On well maintained equipment you typically don't see dramatic changes between EPM's. Always refer to the NETA standards for device testing & insulation resistance limits.
  15. Ceast

    3-pole ATS and breaker trip during transfer

    One more point on the In Phase Monitor type switches. If the gen freq is closely matched to the Normal source it may not drift into the sync window for minutes. I've seen them sit there for 20 minutes. I've instructed customers to check their gen (depending on the governor type) matching speed...