  1. byju1982

    2mx2m 11kV cable tunnel -ventilation method

    Thank you SAK9 ! Happy to know the professional techniques in use around the world. Cable tunnel Hvac engineering indeed requires careful analysis and planning to avoid problems at advanced stages. I am closing the thread now as I got sufficient aspects to think about and proceed. Once again...
  2. byju1982

    2mx2m 11kV cable tunnel -ventilation method

    Thank you Littleinch, MintJulep! That was good information to do some homework. @ IRstuff, top of tunnel is 2meter below road surface.
  3. byju1982

    2mx2m 11kV cable tunnel -ventilation method

    Hi Chicopee, My concern is about temperature rise and associated derating of cables. Thank you.
  4. byju1982

    2mx2m 11kV cable tunnel -ventilation method

    Hi BenMacier, Request to provide some more details. Since it is directly running under the road for 350m, so we are finding it difficult to plan the ventillation. Can the manholes provided for maintenance access be treated as ventillation points ? Thank you !
  5. byju1982

    2mx2m 11kV cable tunnel -ventilation method

    Hello friends! I have 2m x 2m Power cable tunnel running for 300m under a road. It has 11kV cables arranged in trefoil on cable trays approx 50 numbers. What kind of ventillation system should I consider for this tunnel ? Thank you !
  6. byju1982

    Shunt reactor differential stability test

    Hi DTR2011, Yes the CTs are inaccessible and housed inside the turret of the bushings. Thanks.
  7. byju1982

    Shunt reactor differential stability test

    Hi bacon4life, Yes, the same was already completed. thanks.
  8. byju1982

    Shunt reactor differential stability test

    Hi, Is there any method to conduct a differential stability test on Shunt reactor bushing CTs ? I understand that as compared to Transformers , reactor does not have any secondary so shorting on secondary and circulating a current high enough to check the CT secondary current is not possible...
  9. byju1982

    110V DC cable and MCB sizing calculation

    Thanks Scotty ! What is the authoritative standard on this subject ? That is for sizing of DC MCB, DC feeder to trip, alarm-indication and Control circuits.
  10. byju1982

    110V DC cable and MCB sizing calculation

    Hi, We are sizing the DC cables from DC Distribution board to the switch-gear and also the interrupting device (MCBs) at distribution board and load terminal. I understand we should use only the continuous loads for this purpose. Is the momentary load like CB closing coil , trip coil currents...