Generally it is best to measure each cable separately, disconnecting both ends, not as a system. You megger could damage connected equipment, especially in a distribution board!
Now if you have a Y connected xmfr rated at 480V, you can lift the neutral and 500V or even 1000V meg between it and...
Try out this web site:
http://www.deif.com/Products/applications/Switchboard_Instrumentation/Insulation_monitoring.aspx
They have good descriptions on how insulation monitoring works, both for AC and DC systems.
Basically, the meter circulates a small current thru the power system and back to...
You guys are right on: regulator problems.
My guess is your AVR does not have a PF/KVAR regulator.
If not, setting the droop higher might help.
We paralleled for years without PF/VAR regulators: we just set the droop higher. That is, more current, less voltage. As long as you stay in the...
Typically 3 winding xmfs (US standards...don't know your brand) the M/Kva ratings are of the winding. You can look at it like it has 2 secondaries. One you "put in" 7.6M, one you "can get" 6.8M from and one you "can get" .8M from.
We used to use these in remote substations: the third winding...
I agree...you are headed for a replay of the Big Bang Theory!
You say MV: what level? 5KV is much different than 15KV class. I have seen 5KV in unshielded cable: you would never do that with 15KV.
When the PM's the breakers, did they use any cleaner on the insulators? I used to do a lot of...
Took a while, but now it is working fine.
I suspect the utility did some work on their system, but we may never know for sure...???
The circuit breaker had a faulty trip unit leading us to believe it might have been seeing a large unbalance. Plus it was looking at positive sequence currents...
The xmfr z's will sum, making the voltage regulation even worse. I can see this will be a problem.
Check your power system + xmfr + cable voltage drop calculations at 100% and 400% of motor current. You may end up with such poor regulation you will burn up your pump motor.
Any way to start...
So does the inverter use the gen as the starting motor or does it run a separate motor for starting? I have seen both ways, but it makes a big difference in the inverter (LCI vs regular VFD) and the time you have to start.
The amortisseur (starting) windings need to support it: most gens don't...
Commercially available, off the shelf power supply should be availalbe. 400 hz might be a problem, so I would look at a switcher style, not a series pass. Many switchers, while made for 60Hz, will work on 400Hz. You will probably have to ask the mfr.
Or make your own full wave bridge to get...
Good ideas, much appreciated.
I did not know that about unbalanced loads and displaced neutrals, waross, thank you. That makes sense. One of the things we need to pass on to the utility to check.
Subtech: yes, I agree with you. We have asked the utility to check, but I am not sure they would...
DSB: Technically, you are absolutely correct on var flow. But there are a lot of technical folks out there working with sync motors that think increasing excitation moves from lagging to leading because they are used to motors.
Alan: You hit the nail on the head! I tried vector math on the...
Check out COSPP magazine, they have had some good articles.
There are LOTS of methane burning co-gen plants out there: almost every municipal land fill can support a 'trash burner.' Many large feedlots digest the cow's "output" into methane--and some of these can be 1Mw or more!
Most of these...
May I suggest you Google "generator winding pitch" and you will find several very useful articles. No reason to re-print them here.
One of the first hits is a CAT technical paper.
Steve
It looks like induced voltage. Parallel conductors will have distributed capactance all along their path, inducing voltage from one to the other. You said something about DC: if this is from a rectifier or SCR source, the noise and thus induced voltages can be large.
If the other source cannot...
Great feedback, all, thank you!
I'll try to answer your questions.
Alan: I think I will ask them to get a phase angle meter and re-check PT's and CT's. Couldn't hurt. Electrical contractor was not experienced in switchgear work, either.