  1. BoyNaruto

    Transmission Line Sizing

    We are on the process of planning our new fabrication plant and the we need to have 6pcs. 500KVA transformers. The existing High tension on the area is 30,000V. I am not sure of how much is the capacity of the line in terms of Amperage. Upon calculation, each one of my 500KVA transformer would...
  2. BoyNaruto

    Testing of a 380V/280KW 60Hz Motor

    Hi Ozmosis, Thanks for the translation, i've tried using an online translator but it gave me different meaning. I was thinking the generator is really small for my compressor. But I need to defend this by electrical formula or simulation so I can convince my boss. Also, the problem, is that it...
  3. BoyNaruto

    Testing of a 380V/280KW 60Hz Motor

    Hi Bill, Thanks for the quick response. Below are my answers: 1.) Yes the generator's speed drops upon compressor start up (delta to star) and also when air loading. But in between this transition, the generator is at the right speed and voltage output. 2.) Yes when at nominal load, the...
  4. BoyNaruto

    Testing of a 380V/280KW 60Hz Motor

    I just want to add this info, perhaps someone can help me pinpoint where the verdict is. The genset that we are using is just a customized genset. Somebody from the company is clever enough to advice the manager to have a genset made from junks. The V8 Mercedes-Maybach engine came from Swiss...
  5. BoyNaruto

    Testing of a 380V/280KW 60Hz Motor

    Hi Bill thanks for the specs, but the problem is how to defend this one, the compressor in combo with the 400KVA has been working for a while (at least for a month). Once can easily say it was really under specs since when the compressor loads the 10Bar tank, then the generator really is being...
  6. BoyNaruto

    Testing of a 380V/280KW 60Hz Motor

    Dear Masters, I am new to the world of motors, but more or less I can stand the principles. May I ask on how to measure and how to test this big motor that we have for our compressor? Suddenly the start up draws around 500-600A which causes our mains to trip. But when I test the compressor, I...
  7. BoyNaruto

    Checking and Testing of Exciter

    Hi Warross and other professionals, I've managed to check the insulation resistance on the exciter stator field and exciter rotor windings and the result is 0.12M on the stator and on the exciter rotor is only 0.02M. The Main field is about 3-4M and I suspect i don't have problem with this...
  8. BoyNaruto

    Checking and Testing of Exciter

    Hi Waross, Yes I have, I measured the resistance of the exciter stator and its only 2.5ohms. I think I need to check it out with my megger, what could be the minimum allowable resistance? Thanks, Chris
  9. BoyNaruto

    Checking and Testing of Exciter

    Hi, May I ask your technical advise as to how can I test if my exciter stator coil and exciter rotor is still in good shape? I took the resistance reading from the exciter stator and the reading is only 2.5ohms. I understand from my previous readings that normally the stator coil is around...
  10. BoyNaruto

    Stamford Alternator 50-60Hz

    Hi Guys, Got the programming manual from Bernini Engine Control, they have some funny trick on programming though. I've adjusted the Over Frequency Alarm to 65Hz and checked also the over voltage alarm to 500V. After this, I slowly adjusted the engine speed until I get 1800 rpm and continuosly...
  11. BoyNaruto

    Stamford Alternator 50-60Hz

    Hi edison123, Oops I missed that one, from the catalog i gathered from internet, the 380V/50Hz (1500rpm,), will be 416V/60Hz at 1800rpm..... guess we got the wrong generator. :( Scenario is that again, we have 60Hz here in our area, my boss bought a 22KVA UPS for all the computers and he has...
  12. BoyNaruto

    Stamford Alternator 50-60Hz

    Hi edison123, Yeah i understand that, on the voltage regulator, there is a provision for 60Hz operation, alternator's plate tells 50hz with an rpm of 1500. If I adjust to 1800rpm, then from the motor formula I should get 60Hz. But one thing I am not sure of is the mechanical design limits. If I...
  13. BoyNaruto

    Stamford Alternator 50-60Hz

    Guys, I have this stamford alternator from a MOSA generator. The motor plate says 50Hz but I want to operate to 60Hz. Can I adjust the speed of the engine, jumper the voltage regulator to 60Hz and adjust parameter in the engine control? Can this procedure give me 60Hz? Thanks
  14. BoyNaruto

    High Frequency Generator

    Hi Panter, Thanks, good to know I'm not the only one using this HFG... Guess I am stuck with this problem if I cannot justify enough to buy a 20KVA VFD....
  15. BoyNaruto

    High Frequency Generator

    Hi edison123, Yes the rotor side has 4 slip rings, 3P+N. For the Bosch grinders yes, they are also 3P+E.