  1. bouk715

    In-place mortar shear tests

    Thanks dhengr...this is very good feedback. I was a bit surprised to see a number of tests specified in the code as that is usually left up to the EOR's discretion. As far as using different methods of floor/roof attachment - I was coming at this from the direction that I am much more...
  2. bouk715

    In-place mortar shear tests

    I'm working on a project in Massachusetts where the architect is proposing to gut the entire building (5-story building). Building construction generally consists of multi-wythe brick walls with wood-framed floors and roof. Per Massachusetts amendments to the 2009 IEBC, since this is Level 3...
  3. bouk715

    Radiant heat in concrete on composite deck

    Just wanted to post a last follow-up for anyone looking at this post in the future. After quite a bit of searching, I did find an article that provided some recommendations and considerations for radiant heat in composite slab/beam design...
  4. bouk715

    Radiant heat in concrete on composite deck

    Ok...haven're been able to find that recent. I'll look a bit more. Do you recall if it was about radiant heat or just conduit in general?
  5. bouk715

    Radiant heat in concrete on composite deck

    http://www.eng-tips.com/viewthread.cfm?qid=252077 Is this the thread you are recalling?
  6. bouk715

    Radiant heat in concrete on composite deck

    KootK - good info. My recollection is that ASCE 3 is for any type of conduit, so it seems that radiant heat would probably be captured under that. The 18" minimum spacing could be tough too...I'll have to talk with the MEP as I recall that the heating loops usually have a tighter spacing than...
  7. bouk715

    Radiant heat in concrete on composite deck

    Thanks jayrod12...I wasn't able to find anything online or in a thread search, but let me know if you know of something.
  8. bouk715

    Radiant heat in concrete on composite deck

    Thanks for the quick response! Yes, this is an interior slab. 2" deck with 3" of concrete over the top of the deck (5" total thickness).
  9. bouk715

    Radiant heat in concrete on composite deck

    Does anyone know of design guidance for composite slab and composite beam design to incorporate radiant heat tubing? I'm having some trouble finding any design examples/tech notes online. We are designing a floor system with concrete slab on composite metal deck supported by steel beams. The...
  10. bouk715

    Insulrock Roof Deck

    Thanks again KootK. Roof framing is bar joists spanning to steel girders spanning to wide-flange columns. So steel straps may be an alternative depending on the diaphragm loads.
  11. bouk715

    Composite Steel Floor Beams

    Also, I'm not sure what your bay spacing constraints are but you may be better off extending the girder spans to 30'-0" +/-. You could use 2" or 3" composite deck with more concrete (5"-5.5" total) that will give you a bit more mass to dampen vibrations. I've typically used 10'-0" beam...
  12. bouk715

    Composite Steel Floor Beams

    spats - I've found similar results when trying to meet DG11 for composite floors for new schools. Whenever my beam span exceeds around 30'-0", DG11 typically controls the design. I find this especially true when design live loads are 60 psf or less (like office or classroom space). I almost...
  13. bouk715

    Insulrock Roof Deck

    Thanks KootK. The link you posted is where I downloaded the design manual I was referring to. I did find a thread that seems to discuss the Insulrock system and provides a diaphragm shear of 500-1200 plf. But that sounds like a system where the boards are used as forms and they gypsum...
  14. bouk715

    Insulrock Roof Deck

    We're in the preliminary stages (schematic design) of a building renovation. I have existing drawings for the building dated 1964. The architect is proposing to put large roof-top units on the structure surrounded by a screen. The screen area is large enough that it will increase wind loads...
  15. bouk715

    Masonry Design LRFD vs. ASD

    Previous post has LRFD spreadsheet. Here's the ASD one.http://files.engineering.com/getfile.aspx?folder=43886794-b978-4d2b-aa2e-e40249c32985&file=ASD_CMU_shear_wall.pdf