Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by boaterbill

  1. boaterbill

    1-wire single phase to fun 40hp pump with vfd

    Yes you probably can, but the pump motor's VFD will need to be configured for the single phase input. The drive will need to be rated for twice the FLA of the motor. This is because only half of the input rectifiers are available to energize the DC bus. So a 120 amp 40 horse VFD will need to...
  2. boaterbill

    inverter whine

    If the windings of the motor are starting to fail the carrier frequency whine can increase. Also if there is stray currents through the bearings it can make the motor sound louder. I would change the carrier freq and see if the problem noise follows suit.
  3. boaterbill

    Drives at motor's starting up

    The mechanical inertia needs to be determined. A soft start will reduce the strain on the mechaincal equipment as the unit is ramping up. A VFD will operate the motor across different speeds to operate in the process more efficiently. Contact Robicon or Allen-Bradly for the medium voltage info...
  4. boaterbill

    Single Phase to Three Phase VFD

    I would check the buss fuses. I had an ABB ACH 500 do a similar thing about a year ago. Ramp up to about 40-45hz and trip.
  5. boaterbill

    Exhaust Hood VFD Operation

    As each of the manaual dampers open/close, the static setpoint will change. installing a static pressure sensor 2/3 of length of the duct from the fan as in put to the controls will allow the VFD to ramp up/down to maintain the static pressure needed. BTW, the real installation will be lucky...
  6. boaterbill

    Air Cooled Chillers vs Water cooled Chillers

    If you have the potential for dirty water, then why are you considering a chilled water system? If that is such a problem, DX will work. And the chilled water lines are sealed anyway, you always treat the water on installation, so again, why is the cost /quality of water a problem in less than...
  7. boaterbill

    cat5 ethernet, 120V interference

    can you put a divider on your reel? that might seperate the power from ethernet enough to not have problems.
  8. boaterbill

    LV Variable Speed Drive for NEMA Standard Duty Motors

    If the motors are new, the winding insulation should be OK. How long are the motor leads from the VFD? Anything over 100 feet I would put on an output reactor to reduce the harmonic spikes at the motor.
  9. boaterbill

    Need Quick Braking of Induction Motor

    I am not familiar with that drive, but since you are already using Breaking resistors, see if you can also use DC injection braking from the inverter. There should be a paramter setting for this. Good luck
  10. boaterbill

    Sizing bypass contacts for Soft Start

    When the soft-start has ramped the motor to full speed, switching to the bypass contactor will still require the contactor to be able to handle the FLA of the motor. Some bypass contactors are rated to start and stop the motor without the soft-start and are rated for full starting current...