Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by bitoy

  1. bitoy

    Power generation, circulating current problem

    An individual droop CT's should be allowed to feed back to the AVR's. These CT's are short circuited or bypassed through relay contacts during single or isochronous operation.
  2. bitoy

    I was currently troubleshooting a p

    I may say you have two faults to locate. first is that you have a thermally controlled cooling fan on the server unit that could be dried out of lubrication on its bearing or shaft bushing.this is causing a heavy draw of current when its called to run. second is that you have a loose connection...
  3. bitoy

    Isolation contactor on VFD

    You may configure your emergency stop to control both a contactor installed at the input and output of the VFD.This is to insure that the VFD and the motor are totally isolated from power.The VFD is normally run with load or load shall be connected first before command to the VFD to ramp is...
  4. bitoy

    BASE LOAD OPERATION OF GENERATING STATION

    Base load operation of a generating station is sopposed to be a kind of operation with a fix number of a power generators in parallel carrying a load less than their capacity.Or a single generator is operating at a load lower to its capacity and that the load never exceeds the generator capacity.