Recent content by bdf5526

  1. bdf5526

    Generator CT Iron Core Grounding

    Hi, this is the reply from the supplier:- translated from Chinese (Mandarin ) to English. The terms not very correct I guess since I cant read Chinese Mandrarin. "The CT connection shows on the pictures is not for neutral point connection or for CT coil grounding . It is for equal potential...
  2. bdf5526

    Generator CT Iron Core Grounding

    Hello, We have current transformer at neutral point of the generator. Strangely there is a metal braid connection from the body (cast resin) to neutral point phase conductor of the generator. (I assume its for the CT iron core) We have this metal braid from all CTs to its respective phase...
  3. bdf5526

    Micom 633 Operating Data Measurement

    Hello, In our Micom P633 transformer relay, we could not get the "Idiff" and "Irestain". The rest of the measurements are ok. I could be looking as the wrong group as it is on 'FT_DA' (which is fault recorder). If I extract setting in the setting file than I could see the actual reading of...
  4. bdf5526

    MICOM P542 Secondary Injection

    Hi ZabSib, Sorry for very late reply. Yes, it is as what you said. Modification on PSL has solved the problem. Further mode we have also Lorck Our Relay. We also make use of this contact as an Input to give have the trip active. Thanks for the feedback.
  5. bdf5526

    MICOM P542 Secondary Injection

    Hello Guys, Now the client have new request about the tripping sent via fibre optic. They wanted the trip to be latched. From ourside we made the trip send to be latched (intertrip CH 1) is active until we reset at ourside. I am trying to figure it out how to make the trip via Fibre Optic...
  6. bdf5526

    MICOM P542 Secondary Injection

    Hi DiscoP, Thanks for the feedback. The relay address were wrong. We established connection and we did as well send trip to the remote relay. Thanks for the tips.
  7. bdf5526

    MICOM P542 Secondary Injection

    Hi DiscoP, Thanks for the clarification. The transformer rated current current is 794 Amp. CT ratio is: 1200/1 Amp CT secondary rated current 794/1200= 0.66 pu Is1 setting is 0.3xIrated = 0.3x0.66= 0.198 pu I was mixed up. 0.66 amp is the transformer secondary rated current. In the test...
  8. bdf5526

    MICOM P542 Secondary Injection

    Hi DiscoP, Thanks for the feedback. Yes. You are correct the DDB was wrong. I was looking at the manual for Micom P543. After assign the correct DDB the relay tripped for Diff B,C and later A as expected. The thing I tried to understand is when I inject in Phase A, the relay tripped (Idiff A)...
  9. bdf5526

    MICOM P542 Secondary Injection

    Hi All, I have been trying to inject current for Micom P542 and the setting of the relay is: Is1= 0.2 pu Ki= 30% Is2= 2.0 pu I was checking the low set of the cable differential protection function. I did exactly the same like in the manual and the monitoring Bit in the Commissioning Test...
  10. bdf5526

    Micom 633 trafo Diff Relay

    Hi rasevskii, Thanks for the reply. It is a Dny11. We are testing the protection relay and all the secondary injection done from relay terminal at relay cubicle. Soon maybe I will try to inject it with 3 phase current supply and have monitor the differential. But I do not know if it might...
  11. bdf5526

    Micom 633 trafo Diff Relay

    Hi all, Once again I need a advice from gurus here. we need to prove the transformer differential setting to our client. Relay used to protect 2 winding trafo. Diff trip works fine when we inject only at HV winding (winding a)relay CT terminals (single pahse injection and 3 pahse injection)...
  12. bdf5526

    Live 400KV Insulator washing

    Thanks for the feedback guys, Looks like voltage divider and length of the insulator definitely can be related to that scenario.
  13. bdf5526

    Live 400KV Insulator washing

    Hello Guys, On our site 400KV trafo bushing and insulator was cleaned with Online Wet washing last week. The supplier for the washing system was onsite for cleaning. Only for the first time. We had a good water resistivity 5 micro siemens/cm. And at 25bar from the pump cleaning was done with...
  14. bdf5526

    Breaker timing tests

    hi elecpl123, I have attached a file of the GCB close open operation. For this GCB the manufacture take the time between when the NO contact close and opening of the main contact as OPEN CLOSE time. Which is a bit lesser than normal CLOSE OPEN time. maybe somebody can help. Thanks...
  15. bdf5526

    Generator unbalanced current

    Hi warros, I measured the current and I am scared. Neutral point of the Step up has a surge arrester rated for 132kv connected in parellel. No current via the surge arrester grounding when I measure. If I measure at the grounding of the Neutral point I have about 4 Amps (50Hz). Transformer...