  1. apsix

    Reinforcing unreinforced column

    As a_urbs noted the lack of confinement is allowing the spalling. The attached shows a method I've used to provide post-tensioned confinement. In your case, due to the size of the column, extra confinment could be provided with threaded rod through the column, located midway to each face...
  2. apsix

    Simply supported two way slab definition

    The span/effective depth ratio is based on the shorter span, therefore the support condition type is also based on that direction.
  3. apsix

    125x50x2.5 RHS?

    The 1974 edition of the AISC Safe Load Tables notes RHS & SHS as 250 Grade steel, CHS as 200 Grade.
  4. apsix

    foundation pad not deep enough

    Dig a 600 deep hole to determine the soil at that depth. If it's fill (made ground) it's not deep enough. If it's very dense gravel it's all good; show the structural engineer for signoff.
  5. apsix

    Wind loads for a fire water tank

    sdz, my AS1170.0 Table F2 for wind has ARI = 500 years. Do you have the latest version? Mine includes Amendment 5, issued in 2011. Since there is no tank floor it looks like tiedown is required.
  6. apsix

    Wind loads for a fire water tank

    I would say the the probability of the tank being empty and also subject to the design wind event is negligible, hence tiedown shouldn't be required.
  7. apsix

    AS/NZS 1170.2 Cfig for Cylindrical Tank

    Cfig = 0.63 compares well with Table E3, where Cd for cylinders can be as low as 0.6 when b*V > 10 m2/s.
  8. apsix

    AS3600 2017 Draft

    Try this.http://files.engineering.com/getfile.aspx?folder=dc16a30c-ee9e-42c9-b9f4-00a2a25225a4&file=draft_AS-3600_Public-Comment.pdf.pdf
  9. apsix

    External Pressure Coefficient (AS/NZS 1170.2)

    Strict interpretation could mean that interpolation shouldn't be done in that case, but I DO use 0.0 to interpolate. This would seem to agree with the logic of the rule.
  10. apsix

    AS/NZS 1170.2: Local Pressure Factor

    The BAR is actually defined as the average roof height (h) divided by the smaller of b or d, ie the smaller plan dimension. The reference number on the diagram is a representative location for the associated Kl. There are multiple elements with multiple factors, but they are assessed in...
  11. apsix

    Load factors AS 5100

    Or for a cantilevered beam; dead load on the cantilever reduces safety while on the backspan it increases safety.
  12. apsix

    No backspan 6 ft long concrete cantilever

    A generously sized fillet at the wall-slab junction will help detailing of the joint. 16" doesn't seem overly generous if the wall is cantilevering, hopefully it can also span horizontally.
  13. apsix

    When columns are in compression why do we need then reinforcement?

    A666 Think of a test cylinder only loaded to 50% of its failure load; it's like a small column with a Factor of Safety of 2.
  14. apsix

    What is the difference between BS 8110-1:1997 and BS EN 1992-1-1:2004+A1:2014

    No difference, just the Eurocodes are a subset of the Euronorms.