Recent content by aolalde

  1. aolalde

    Cryogenic cleaning of motors & generators

    Hi Edison123. We have recently blasted a ball mill synchronous motor 3000 HP 32 poles. the rotor was partially removed to reach the windings. Dry ice blasting cleaned nicely the areas reached by the blasting but did not well at the hidden areas between top and bottom conductors. The extreme low...
  2. aolalde

    700 kw motor started with a soft start

    You will go to the motor and pump speed-torque curves to calculate the starting time required to reach full speed under the nominal or the reduced voltage applied to the motor. But you need the total inertia (motor+pump+coupling) to be accelerated (WK2) (Lb*Ftsq) And yes, your motor torque...
  3. aolalde

    Number of start of high voltage motor

    For "High Voltage Motors" the manufacturer designs the number of starts that the motor can endure before thermal damage is developed. They comply the standard of manufacture or the customer requests. The number of starts is close linked to the load inertia since the starting time and the heat...
  4. aolalde

    1909 GE 15 hp wound rotor controller T 133 R

    http://i35.tinypic.com/2vrzpeb.jpg An open delta or V connection could work with 2 contactors per step . The currents are nor balanced. .
  5. aolalde

    What correction factor for - 4 deg C motor rating?

    Standard NEMA MG1 Part 14 defines USUAL SERVICE CONDITIONS. Environmental Conditions Machines shall be designed for the following operating site conditions, unless other conditions are specified by the purchaser. a. Exposure to an ambient temperature in the range of –15°C to 40 °C or, when...
  6. aolalde

    AC motor turn into a generator..

    Only (as synchronous machine) the residual magnetism (phi)in the rotor core could generate very reduced voltage since e= -N d(phi)/dt, and phi---> 0
  7. aolalde

    Running a motor on Low Voltage

    The voltage reduction (57.73%) due to the wye reconnection will drop the torque similar to the sample lower curve. The load torque will produce high speed SLIP. If the load torque exceeds the new reduced breakdown torque, the motor shaft will stall and the current goes to the locked rotor...
  8. aolalde

    Induction Motor Heat Generation Calculation

    By definition an electric motor converts electric power into mechanical power. The motor losses is the part of electric energy that is converted to heat and it is proportional to the motor efficiency, with exception of the mechanical energy required by the self propelled motor air cooling fans.
  9. aolalde

    Motor Temperature Rating

    The temperature shall be measured in the windings, not the external motor surface. Taking the resistance of one phase with the motor at room temperature and then comparing it to the same phase resistance after working the motor under load is a way to measure the winding temperature. See IEEE Std...
  10. aolalde

    Winding Data

    Hello joebems: The winding seems good for 2 poles. The magnetic load shows average flux densities. 59 kL/sqin in the air gap, 116 kL/sqin in the back iron and 104 kL/sqin in the teeth. The Circular mils per ampere are around 267 for the wires posted.However if you drop a single turn the...
  11. aolalde

    Wire Quality Inspection

    Consult NEMA Std Publication No. MW 1000, Magnet Wire.
  12. aolalde

    Water Cooled Machine IC81W

    As WARoss stated, accuracy of temperature and water flow rate measurements is very important. The water temperature rise is pretty straight to measure the energy it removes from the heat source. It takes 1 calorie (4.184 joules) to increase 1 gram of water 1 °C.
  13. aolalde

    Water Cooled Machine IC81W

    kWloss = (liters/sec) x ( delta T) / 0.24 for water. Since 9.4 cum/hr = 2.611 liters/sec, and delta T = 39-33 °C = 6 C kWloss = 2.611 x 6 / 0.24 = 65.275 kilowatts.
  14. aolalde

    convert a slip ring motor into a variable voltage transformer?

    The phase angle displacement is dependent on the number of poles (P).In general G° = E°/P/2 For 2 poles the geometric degrees (G°) are the same as the electrical degrees (E°). For 8 poles to displace 90°E you move 90/8/2 = 22.5 ° geometric. WRIM = Wound Rotor Induction Motor.
  15. aolalde

    reducing voltage to three-phase induction motors

    At 75% load assuming the power factor will be reduced around 10 points or PF = 86.5 % at full voltage and due to the flux reduction it keeps the 87.5 with reduced voltage and 75% load and no change in efficiency ( very optimistic). At full voltage, the current I1= (0.746* 400*.75) / (1.73...