  1. Addy71

    Experience with LIRA for cable assessment

    Does anyone have experience with using LIRA (Line Impedance Resonance Analysis) for cable testing & has compared the results with TDR, VLF tan delta & partial discharge? We are doing the latter & client wants a comparison. To my understanding, LIRA can detect physical damage to the cable but...
  2. Addy71

    motor/gen HV testing. DC or AC HV?

    We use a DC Hipot tester (Phenix) as well as a power frequency tan delta tester (Tettex + Eltel) & a PD analyzer (PD Tech + HVPD). We have wondered about purchasing a VLF source to avoid the resonators; but I am unsure if the tan delta values plus PD values & patterns at power frequency would be...
  3. Addy71

    Interpratation of the online Partial Discharge Measurement Result

    I think the more important questions are: 1. What is the coupler rating - 80 pF, 500 pF, 1 nF, 2 nF or 8 nF? - The higher the coupler rating; the larger the measured signal will be. 2. What is the frequency band in which the measurement is taken? - A lower "low cut-off" frequency will give you...
  4. Addy71

    high P.I. (with good one-minute I.R.)

    I have added it as a PDF now, should work.http://files.engineering.com/getfile.aspx?folder=dea3bb2b-ac7b-4fb5-b56c-7760bb6142c8&file=P43_October-10_R8_IR_&_PI_Draft_Standard.pdf
  5. Addy71

    high P.I. (with good one-minute I.R.)

    IEEE 43 Draft Standardhttp://files.engineering.com/getfile.aspx?folder=920e3df2-de41-4324-93e0-9a255c3f0aac&file=P43_October-10_R8_IR_&_PI_Draft_Standard.docx
  6. Addy71

    high P.I. (with good one-minute I.R.)

    I would agree with EPete that extremely high P. I. values do indicate insulation degradation. I have attached data of two identical 9.2 MW, 13.8 kV motors that I tested some months ago. These have been examined and visual indications of degradation & PD observed. A spare motor is being planned...
  7. Addy71

    high P.I. (with good one-minute I.R.)

    Here’s an explanation of Dielectric Discharge Ratio from Metrel’s “Guide to Modern Insulation Testing”: The dielectric discharge test is very useful for testing a multi-layer insulation. This test can identify excess discharge currents that occur when one layer of a multi-layer insulation is...
  8. Addy71

    high P.I. (with good one-minute I.R.)

    Here another case; this one does worry me. These are identical 30 MW, 11 kV, 2-pole gas turbine generators; commissioned in 1995. The P. I. values for two phases increased drastically for GTG 1. We've opened the generator; cleaned it (solvents + dry ice), dried it & varnished it. The P. I...
  9. Addy71

    high P.I. (with good one-minute I.R.)

    The motors are all of 6.6 kV. I do not know for sure that stress grading coatings are present; but this is quite standard for 6.6 kV motors (certainly for the first two; which are of BHEL make). The top row is for October 2012, bottom row for October 2011. Why the query about stress grading...
  10. Addy71

    high P.I. (with good one-minute I.R.)

    ElectricPete, I have seen this kind of behaviour & have seen the correlation in the capacitance & tan delta tip-ups (see the attached document). The top reading for each motor is of 2012 & the bottom reading is for 2011. Couple of these are planned for rewinds. These motors are 6.6 kV with VPI...
  11. Addy71

    Non-magnetic Retaining Rings removal from 2 pole generator rotor

    There is no way that the rotor retaining rings don't have locks, just need to find them. Some have external nuts; other have circlips. Some have both. Often; the circlip won't release till you cross 200 C. I've always used gas torches, work just fine. Induction heating equipment is a lot more...
  12. Addy71

    TVA/Corona Probe Suppliers

    PD locations based on PD Tech guidelineshttp://files.engineering.com/getfile.aspx?folder=1ad79eaa-9f45-428a-a090-da168abb6897&file=Partial_Discharge_Locations.pdf
  13. Addy71

    TVA/Corona Probe Suppliers

    PD Interpretation based on PD Tech guidelineshttp://files.engineering.com/getfile.aspx?folder=0d4e69dd-0766-4457-ae54-bbbb3229306a&file=Partial_Discharge_Interpretation.pdf
  14. Addy71

    TVA/Corona Probe Suppliers

    Hi EPete, Thanks for the slides. So, I understand that you do TVA probe checks only if the Iris system shows high values. Is that correct? I have attached a presentation explaining the cause of +ve & -ve pulses, by Cutler-Hammer. It is most logical. I get confused at times as PD Tech uses...
  15. Addy71

    TVA/Corona Probe Suppliers

    EPete, Thanks for the feedback. A few questions please: 1. I have been recommending swapping the line & neutral leads to many clients in India but no one takes it seriously. Is this a standard practice in USA? 2. For these particular 13.2 kV motors; do you have a phase-resolved PD pattern...