Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by Adamito

  1. Adamito

    Ground Grid outside or inside building?

    I might be wrong but it looks simple to me. Why not just put those rods deeper so it is below permafrost. I don`t know how deep this permafrost is, but if it is easy to get underneath it, you'll have as much efficiency as anywhere else(I am guessing the conductivity underneath is good) .
  2. Adamito

    Neutral conductor dimensioning

    As a 3 phase system is designed, all currents of a resistive load cancel as the sum of all 3 voltages is 0. So for linear, 3 phase loads or a big amount of linear and consistent 12 phase loads, the total current on the neutral should be very low compare to phase currents. Those office buildings...
  3. Adamito

    SWER (Single-Wire Earth Return)

    Hi, I've just learned how a SWER system works, but there's still a few things I don't understand. How can you get a decent efficiency with all your current going trough earth? The ground must be a huge resistance for the current that has to go through many kilometers through ground to come...
  4. Adamito

    Power to Micrologix 1500

    Ok, I should have seen that the power supply supplies 24VDC to the PLC. Outside of that, it doesn't give me information. I forgot to mention that I have a display (PanelView 600)fed from that power supply with 24VDC and it works properly.
  5. Adamito

    Power to Micrologix 1500

    Hello Guys, I am facing a very basic problem with the Micrologix 1500. It is powered via a power supply connected to the PLC via a power cord. When I power it up, I get power to the power supply and its green light turns on. But there is no sign of power on the PLC side. All lights are turned...
  6. Adamito

    three phase motots

    As long as I know, you should choose the higher voltage available on site. This is simply a matter of decreasing the current in the motor, meaning smaller and cheaper wires. Adam Engineer-in-Training
  7. Adamito

    480V Wye Vs Delta Distribution Panels

    As I am just out of school, I still don't understand a few things: As I understand it, a slash breaker cannot be used for 3 wires equipment because it has to support line-to-line Voltage instead of just line-to-ground. If I am right, then why do a 3W panel connected to a 4W solidly grounded...