anoter- Understand Case1. That is what I currently assume. Re: Case2 and Case3 I'm confused. If the bus ties are open, wouldn't the Zeq at any of the busses only be Z1, or Z2, or Z3? or did you mean to state that the bus ties were closed for Case2 and Case3?
Typically I assume that the buss ties are negligible and therefore Z1, Z2 and Z3 are easily paralleled for Zeq. I was just looking to understand how to compute if I were to assume buss tie impedance.
Sorry if you might have misunderstood. This is not for homework. Just looking to do something by long-hand rather than always using EasyPower, EDSA, or SKM. This is not my usual set of calculations. Looking to better understand what I may not have been taught properly before.
I'm attempting to calculate Zeq at the buss level. I have three generator impedances (Z1, Z2, Z3) connected in parallel and the cable impedances (Z12, Z23) connecting each of the generator busses. How do I calculate Zeq at the buss? Are they all in parallel or something else?
Z1 nodes 0-1
Z2...
Not certain if this is the place to post, but...I'm looking for something that I might be able to better help me pull together a document for a land based test site electrical equipment (panels, cable) installation that identifies procedures related to safety, commissioning/checkout...
I have a 3-Ph motor controller for 200-240V. I only have 120V 1-Ph available. In an effort to program the inverter prior to installation, the inverter is able to function with 240V across L1 and L3 terminals. Not looking to connect motor yet, just preset the drive parameters.
I had cut an...
I was just typing as it came across. I noticed you mentioned rewound, and I was thinking for rewire! It is an isolation transformer, 117/117V, single phase, 6A, with a shield. Looking to use it to get 220-240V to an outlet. Not a permanent installation, just a shop toy.
General question regarding PWM VFD (inverter)operation. Using the constant torque setting (V/f), does the input current of the inverter increase as the output frequency increases? and if so, then is it proportional to the output frequency?
davidbeach-
7anoter4-
The following is an abbreviated version from an IEEE Std ., which is the basis for our calculations. When sizing the feeder cables, spares are included when determining the panel demand load which is the basis for sizing the circuit protection and feeder cable size.
If...
rbulsara-
I do not believe that I had mentioned anything about a heater! The load is not a motor, not heater rather power supply or rack of supplies. My original inquiry was regarding the method for determining the load of the feeder neglecting any spares or demand factors to determine...
VTer:
A1: The power panel is fed from a transformer bank consisting of (3)10kVA 480/120VAC single phase transformers connected to provide 3-Ph 3-Wire delta power to the panel.
A2: In this case I agree with your approach for estimating assuming that the loads are closely balanced. If the loads...
I have a 3-Ph 120VAC Delta connected power panel. I was given a method for calculating/estimating the panel feeder cable 3-Ph load ampacity. My question is, how accurate is this method below?
The 3 phase load was calculated as follows; for an unbalanced load on a panel, add the two highest...