I have a background in designing PEB's and mini storage light gauge steel structures.
In my experience I have used either diagonal rods or diagonal flat strap bracing for my flexible diaphragms when using steel roof decking that is NOT shear rated: typical standing seam roof.
I'm reviewing...
The structure has both 8" & 12" cmu block (2000psi) x 24 to 34 feet high. Footing is 24" & 30" wide x 16" deep. Adjacent mat slab is 8" or 18" thick with #5 @ 12" OC or #3 bars @ 16" OC ea way top & btm. Seismic design category 'D'.
My thoughts are that the dowels are for out of plane forces...
I'm performing a plan review.
Example: 8" slab w/#3 bars @ 18" oc ea way & #4 dowels (from CMU wall) @ 24" oc. (obviously different spacing)
Does this fly?
I've typically always required/designed my slab steel and dowels to the same spacing for lapping together.
I've always had the...
I'd like to thank everyone who gave input. It's pretty amazing in the engineering field how many factors are involved in proper engineering design. I learned something and am grateful and appreciate your helping me to grow.
Jon
msquared48,
Thanks for the input! The structure is similar to a Super WalMart in design, except reinforcedd concrete walls instead of CMU walls.
Your comment: "That's a new one on me. I would never do it. It would drive up the required lateral force significantly." Are you saying you would...
This site is in Calif. site class 'D'. Temperatures range from freezing to 120 degrees fahrenheit.
I'm performing a plan check review. I've used cross bracing as well as standard steel decking with diaphragm capacities. My original concern is that the columns, which are spaced at 50 ft OC each...
IBC 2006 section 2305.2.3 gives ratios for maximum diaphragm dimensions for wooden structures.
Is there a maximum diaphragm dimension for a roof diaphragm with VERCO steel deck attached to reinforced concrete shear walls?
Thanks
"In general direct shear is not the correct method assumed for shear transfer in base plates" - jsdpe25684
What is the determining factor as to whether you should use direct shear for base plates or not?