×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

LV Cables

LV Cables

LV Cables

(OP)
Hi All

Could you please give me the minimum insulation resistance of 415V cables (power) and the standard which applies.

Thanks

RE: LV Cables

NETA spec is 200 megohms minimum for 600V and below at 1kV test voltage.

RE: LV Cables

If the cables are to be used for a motor, IEEE Std. 43 recommends that minimum insulation in megohms be greater than machine rating in kilovolts plus 1.  So for 415V, you'd need 1.415 Megohm minimum insulation resistance.

RE: LV Cables

(OP)
Thank you Dandel and eemotor

RE: LV Cables

(OP)
eemotor

Whilest a industry practice is to accept kV+1 MegOhms as acceptable minimum the IEEE43 has changed. For equipment built after 1970 the IR minimum is 100MegOhm for one minute.

Could you please point me in the right direction as to which clause in IEEE43 states that for cables used for a motor should be kV+1 MEgohms.

Or by engineering judgement do we have to accept the minimum value for cables as that of the motors also. I agree with this judgement. We cannot have two values anyway. One for the motor and one for the cable.

The only issue is that cables for LV motors are either PVC or XLPE whilst some motors may be class F in worst ambient condition.

Could you please comment.
Thanks

RE: LV Cables

(OP)
busbar

There is a new revised version of IEEE43 which is IEEE43-2000. I have read this copy and it does not talk about cables but motors.

Any comments on the cable insulation please.

Thanks

RE: LV Cables


At shop.ieee.org, enter 43-2000 in the search field.
  

RE: LV Cables

(OP)
busbar

I requested comments on the IR not shopping details. Please read my last comment.

Thanks anyway.

RE: LV Cables

The reference to Std. 43 was taken from NEMA Standards Publication MG 1-1998 (Rev. 3, 2002).  12.62 (b) of NEMA MG 1-1998 states "Using 500 volts direct-current, take a 10 minute insulation resistance measurement. The insulation
resistance value shall be not less than the minimum recommended in IEEE Std 43. (Insulation
resistance in megohms = machine rated kilovolts plus 1.)"  However, as you mentioned, this does not specifically indicate the minimum insulation requirements for power cables.  This is more of a winding specification.

RE: LV Cables

(OP)
eemotor

Thanks and that was quite helpful.

Would you please give me the formula for calculating the IR in terms of insulation material constant, diameter etc. There are no values specified in any documents except for the works testing methods. It is not a question of installing the cable and forgeting until it fails.

As said my view is that the cable IR should not be less than that of the equipment to which it is connected. Can we accept a different lower value?

Any comments welcome please.

Thanks eemotor again

RE: LV Cables

Guys

As you state that the voltage is 415V, I assume you are therefore referring to a UK system, this would therefore come under the IEE Regulations (BS 7671) not the NEC, NEMA or IEEE43 (not that there is anything wrong with those standards - they just dont generally apply in the UK).

BS 7671 Reg 713-4, Table 71A Applies

For an LV (415V) system,  the DC test voltage should be 500V and the minimum resistance should be 0.5 Megohm, in practice is is unlikely that the actual reading should be anywhere as near as low as this anyway unless you have an old cable.

Above 500V, the DC test voltage required is 1000V and the minimum acceptable reading would be 1 Megohm.

Hope this helps.


_______________________________________
Regards -

Colin J Flatters
Consulting Engineer & Project Manager

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources