Pole Transformer Ratings

Pole Transformer Ratings

Pole Transformer Ratings

(OP)
Someone made a statement to me that the typical can type pole transformers can be safely overloaded by 50%.  Anyone have any opinion on that statement.

RE: Pole Transformer Ratings


One reference is IEEE C57.91-1995 Guide for Loading Mineral-Oil-Immersed Transformers
  

RE: Pole Transformer Ratings

Loading at 150% of rated would not be unusual for a typical load profile.  The rating is based on constant load and if the load is below rating for most of the day, the transformer can be overloaded for a couple hours with no loss of life.

Utilities may also find that allowing the load to reach a point where there is some loss of life can be more economical than replacement.  The utility I used to work for had a loading policy of loading to 125% initially and replacement at 225%.  This was based on a life cycle cost analysis that took loss of life into account, based on the standard referenced by busbar.

RE: Pole Transformer Ratings

Normally, a transformer of this type can carry 300% of its normal rating for a short time without damage, and 150% of its rating for several hours without overheating.

The real deciding factor is where do you live, and what season is it?  During the winter months transformers may be overloaded in the 200% range for several hours without any damage if you live in a "winter-wonder-land" such as I do.

I.e. ambient temperature is the key.

Regards,
TULUM

RE: Pole Transformer Ratings

(OP)
Thanks for the opinions.  Bottom line appears to be that although I can overload to 50% for short periods,  I would not want to run the transformers continuously overloaded, particularly when the weather gets warm.  Secondly, there is nothing special about pole-type transformers.  They just folow the rules of normal liquid-filled transformers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources