Someone made a statement to me that the typical can type pole transformers can be safely overloaded by 50%. Anyone have any opinion on that statement.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Pole Transformer Ratings
One reference is IEEE C57.91-1995 Guide for Loading Mineral-Oil-Immersed Transformers
RE: Pole Transformer Ratings
Utilities may also find that allowing the load to reach a point where there is some loss of life can be more economical than replacement. The utility I used to work for had a loading policy of loading to 125% initially and replacement at 225%. This was based on a life cycle cost analysis that took loss of life into account, based on the standard referenced by busbar.
RE: Pole Transformer Ratings
The real deciding factor is where do you live, and what season is it? During the winter months transformers may be overloaded in the 200% range for several hours without any damage if you live in a "winter-wonder-land" such as I do.
I.e. ambient temperature is the key.