Mysterious Breaker Operations

Mysterious Breaker Operations

Mysterious Breaker Operations

(OP)
A three year old commercial facility recently began experiencing a problem with molded case breakers opening for no apparent reason.  In almost all cases, the breakers open they do not trip!  The breakers are all Square D "homeline" (a residential grade) or type QO (a commercial grade) and range in size from 225A two pole to 20A single pole.  The problem began happening at random about 10 weeks ago.  All breakers are fed from a common 120/240 single phase transformer.

There is considerable evidence that the most likely cause; deliberate human actions, does not explain what is happening.  Extensive efforts are underway to find an explanation and I'm not looking for suggestions on how to proceed in that regard.  I am asking if anyone has experience with a similar situation.

RE: Mysterious Breaker Operations

What does Square D say?  These small molded case breakers are a commodity and not built with the same level of quality as larger breakers.  This is true regardless of manufacturer.  A surprising number of these small breakers fail acceptance testing right out of the box.  

What percentage of the breakers are doing this?  I'd try replacing a few of the bad actors.  If the replacements seem to work OK, I would lean on Square D for an explanation.  

I don't think it is a power quality issue.  Sounds more like a manufacturing or design issue.  Are the breakers subject to temperature extremes, vibration or particulate contamination?  

I'd still be suspicious of a human cause.  

RE: Mysterious Breaker Operations

(OP)
The most troublesome panel had all the breakers replaced.  When that didn't work, the panel itself was replaced with different style breakers along with the service conductors, the utility drop, the utility service transformer, and anything else they could think of.  Enough ground rods have been driven to make it the lowest reading service within miles.  At least 10 "eyewitnesses" to the openings have been identified.  When I was called in by the utility, they said there was an internal debate as to whether they needed yet another so-called expert or an exorcist.

RE: Mysterious Breaker Operations

That's very strange.  It sounds like all of the obvious things have been tried.  

So when you say the breakesrs are opening, not tripping, do you mean the breakers are found in the full OPEN position, not in the intermediate TRIPPED position?  If this is the case, I don't see how it can be a power quality issue.  


RE: Mysterious Breaker Operations

(OP)
Correct, the breaker handle goes to the off position.  There is no need to reset it before reclosing.

With regard to the exorcist, the jury is still out.

RE: Mysterious Breaker Operations

Amazing problem.  I may have to dig up a spare breaker and take it apart to see what would have to happen for it to do that.

Make sure you post the answer when you find it.

Barry1961

RE: Mysterious Breaker Operations

/Check your loads. Is your system generating harmonics.  Usually it's just odd harmonics heating the neutral but it could be spikes or a harmonic componet.  Lot of black magic and voodoo with harmonics. They best thing is to use a recording current meter on selected circuits and watch watch what happens.

Did you add any equipment or have it worked on about the time this started?  Are the trips coincidential with any operations, such as starting process equipment, computers, coffee pots etc?
Do you have any office funiture systems that you feeding.
Are you voltage levels ok?  

RE: Mysterious Breaker Operations

This is not the first time I have heard of this problem.  In my experience with moulded case circuit breakers, the only thing that will turn them "off" is a deliberate switching action.

We provided this advice to an industrial client and after they took action to prevent human intervention the problem went away.


You say that "There is considerable evidence that the most likely cause; deliberate human actions, does not explain what is happening."  What evidence do you have to suggest that deliberate human action is not involved?


RE: Mysterious Breaker Operations

I can't think of a possible cause other than someone opening the breaker manually.  It just doesn't have the necessary stored energy to move the handle to the OPEN position by itself, no matter what scenario I can think of.  

You might try a hidden video camera, if that hasn't been tried already.  Something smells fishy.  

RE: Mysterious Breaker Operations


Very long shot — It may be possible to trip small circuit breakers with mechanical shock, like striking the enclosure or its supports with a mallet.
  

RE: Mysterious Breaker Operations

(OP)
I'm going to be out of town for a few days and won't be able to followup until next week.  Will definitely post if a believable solution comes about.

I would add the comment that in most situations like this one, the true solution has to "overcome" all the bad "facts" that are presented.  I remain highly skeptical of the "off" versus "tripped" issue as well.

Human beings can often be lousy eyewitnesses!

RE: Mysterious Breaker Operations

PWR
Doh! I missed the part about them being in the off position.  
Try putting something on the breaker handles.  Maby a small amount of silicon grease brushed on with  vertical brush strokes.  You don't want them to see or notice the stuff but a purposeful operation of the breaker will show up.
You could also put something on the door or the door operating handle.  Jame Bond used a strand of his hair in one movie.  
They use to sell flourscent powder to put on things to see was stealing them.  I think they stopped selling the powder because it gave people diahera.


“When you eliminate the impossible, whatever you have left, no matter how improbable, must be the truth."  
Sherlock Holmes


RE: Mysterious Breaker Operations

I'm going to vote for the human intervention factor. All the harmonics, thermal, vibration, surge or other explainations would or could cause a Trip, but the way the mechanisms are aligned inside, the breaker handle cannot go into the Off pposition easily unless physically moved it there. The mechanism that is used to Reset after a trip is engaged even if it is a "normal" Off move, and that requires considerable physical force to overcome, probably even more than a poltergiest can muster. The only other explaination might be that they are remote controlled breakers and you did not know that, but these would be rather obvious because they have a small motor attached to each one.

Tug-tug... someone is pulling your leg...

"Venditori de oleum-vipera non vigere excordis populi"


RE: Mysterious Breaker Operations

I have personally experienced a similar situation.  The end conclusion was that when a near by co-gen plant was experiencing some vibration problems with thier mechanical equipment it would create a resonant vibration in the breaker panels.  We determined this by installing a vibration monitor on the effected panels.  The trips occurred during periods of high vibration.

Another facility had a problem that once a month on the same day (the third Thursday)several breakers in this one particular panel would trip. Investigation revealed that when the UPS service man opened the ups cover for an inspection, the cooling fans would cavitate causing the breakers to trip.  The breakers were on a different circuit in a different room from the UPS.

Bottom Line______ Check for vibration  

RE: Mysterious Breaker Operations

Now THAT is interesting, although I have had circuit breakers in panels mounted directly to the sides of portable rock crushers and have never seen that problem. The resonant frequency issue raises the possibility however. Rock Crushers operate on fairly low frequency vibrations, albeit high amplitude.

"Venditori de oleum-vipera non vigere excordis populi"


RE: Mysterious Breaker Operations

Talk about wierd...

Read about an incident in a hospital where the cleaner unplugged a lead to plug in her floor burnisher, only trouble was that the room had run out of points and the nurse had plugged in an IV pump to a point fed from this extension. Patients IV was unaffected as it had battery back up inside but when the nurse saw the unplugged lead there was a huge investigation...

sometimes its the simplist things that fox us, and human error is soemthing that has to be understood. If it can be done some time it will be done, and you must prepare for that eventuality.

Rugged

RE: Mysterious Breaker Operations

I can believe that a molded case breaker could **trip** due to vibration.  I do not see how it could move to the OPEN position due to vibration

In the original problem, it was reported that the breakers were found in the OPEN, not the TRIPPED position.  

The simplest explanation is the most likely - manual operation.  

RE: Mysterious Breaker Operations

If you want to rule out human intervention try installing a lock to the breaker box.

RE: Mysterious Breaker Operations

The lock on the box is easily messed about with, if the MCB is feeding a final circuit with sockets good old Joe Public sometimes puts in an 'accidental' short to trip it out. Seen this done to kill the lights in an area. Then guy mugged anyone going through in the safety of the darkness.

Rugged

RE: Mysterious Breaker Operations

I'm with you dpc, I still think it can't move all the way to the Off position, it would be in the Trip position. It takes extra force to finish the job.

"Venditori de oleum-vipera non vigere excordis populi"


RE: Mysterious Breaker Operations

this is a long shot, but what if your wiring run a way that would create a loop around your box. could it be possible that one of your high amp. motors might be going bad and be drawing more amps at higher loads enough to create an electro-magnet,creating sort of a soloniod.?
there is some iron present in breakers.im not sure if the base of the switch is reinforced with steel. but you can pick up a breaker with a magnet. with it not being human, this is the only other thing i can dream up. good luck.

RE: Mysterious Breaker Operations

(OP)
Epilogue

There has been no resolution to the problem even though several weeks have passed since an "incident" occurred.

Since my last posting I spoke with an individual who had two Dranetz power monitors connected and they detected nothing as the four main breakers for each business opened at the same time while he stood three feet away.  Multiple witnesses have described being directly in front of the one panelboard that gives the most trouble while a few to all of the breakers open at the same time.

The owner ran the building off a generator for a week and no incidents occurred during that week.  Since then, it has been put back on the utility service and a little over two weeks have passed without problem.

I certainly will not be surprised if the problem returns.  

The fact that these breakers open and do not trip leads me to believe that a satisfactory physical explanation will not be obtained.

RE: Mysterious Breaker Operations

Just a thought.The next time one of these breakers do this ,reset it then trip it iether with load and or short.You may find that this is just how that breaker works.I have installed breakers from every manufacturer and sometimes they do trip into the off position.The square d home line breakers have not shown themselves to be of the same quality as the older window flag type.
Just a thought

RE: Mysterious Breaker Operations

use a time delay relay and check the behaviour of any one breaker if not trip then o.k.check ur neutral connection also.

RE: Mysterious Breaker Operations

telasin's got the right answer. Part of it, at least.

Some breakers have NO CENTER POSITION. They trip to OFF, the trip action opens the contacts and resets the mechanism in one continuous move. This is common on miniature circuit breakers, both residential and commerical.

I worked at a Cutler-Hammer plant for some years. Cutler-Hammer bought Westinghouse's breaker business. In the same plant, residential breakers that were originally Westinghouse tripped to a center position. Residential MCBs that were originally from CH tripped to OFF. Some exceptions were available on the CH side, where the breaker tripped to a center position. These breakers represented a small fraction of the original CH branch.

Contact SquareD, they'll let you know if these breakers trip to OFF. By the looks of your case I'm pretty sure the answer will be 'yes'. Maybe you have both types of breakers and see some tripping to the center while others trip to OFF. If so, such a mix-up of product would confuse anyone.

Now, the other question is why they are tripping. Before vibrations, I would actually look for temperature issues. Miniature circuit breakers are very susceptible to ambient temperature. Although I believe SquareD has made some patented innovations that address the problem, it is possible they are still tripping because of high temperature. Look for stuff like:

1. Has the customer load increased sharply in a brief period of time? This would increase heat in electrical rooms.

2. Are the terminals on the breakers tight? Loose connections create unnecessary heat. If no maintenance is ever performed, you could have many terminals that need to be tightened.

3. Have the electrical rooms changed in any way recently? Has ventilation to the room been obstructed?

4. Do the breakers trip during a certain time of the day? Does the sun hit the roof of the room more now than in the past (construction changes)? Or are they tripping due to a rise in customer demand?

5. Are there new loads connected to the panels? The addition of several new circuits will increase the temperature in the panel.

6. Are the breakers old? Old stock could have dirty contacts that would increase the temperature in the breaker. Yet, I find it highly unlikely that a high amount of breakers would start to act in this way at the same time. I would look for general sources of heat in the room, or new circuits.

The upper limit for temperature requirements is set by UL in the Y programme of I forget which standard. MCBs have to work indefinitely without tripping at 40 deg C under 100% of rated current. For practical reasons 'indefinitely' is taken as 1-2 hours. After that most breakers have normalised to an even level somewhere above 40C. Exceed the temperature or the current and you're in uncharted territory.

RE: Mysterious Breaker Operations

Did you say even the 225A breakers were doing this?

RE: Mysterious Breaker Operations

Square D type QO breakers have distinct TRIPPED position and must be moved from TRIPPED to OFF before the can be closed again.

RE: Mysterious Breaker Operations

First some questions:

1. Are your lights controlled by means of the circuit breakers instead of with light switches? If somebody is getting enough sunlight they could be cutting the power for the sake of their eyes. He or she could also be someone who never remembers  which circuit breaker needs to be turned off and just turns off breakers until they hit the right one.

2. Was anybody hired right before this started happening?

I have been able to demonstrate to myself that vibration alone will trip a QO circuit breaker. Just hold QO115 or QO120 in your hand without anything connected, put the handle in the on position, and shake. Just the right shake will cause the circuit breaker to trip. This will happen to ANY circuit breaker that has a 1/2 to 1 cycle pickup and clear time on short circuits. Even General Electric 15 amp and 20 amp circuit breakers will do this.

How much vibration it will take without tripping depends considerably on the magnetic trip setting for short circuits. For a 15 amps circuit breaker the magnetic trip is around 150 amps and to get a 1/2 to 1 cycle clear time at that current level requires the circuit breaker to be as sensitive as a conventional mousetrap!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources