Sprinklers in a library with minimal clearences

Sprinklers in a library with minimal clearences

Sprinklers in a library with minimal clearences

(OP)
I am looking at a sprinkler design in a library where they want to place the books so that the top books are within 0.25" from the ceiling.  Also, the ceilings are the same as the floor above (concrete) and they are only about 7' high.

They want a preaction system due to concerns with vandalism.

Looking at NFPA 13, I cannot see how this will be done with the stack height they want.

I have two questions.

1.  Anybody know of a way that can work with this while staying within the prescriptive parameters of the code?

2.  If not, has anybody ever tried to get a variance or appeal the code requirements?

Option #2 might be the route if it is possible.  The client is a major university.  Therefore, they do have some clout when it comes to getting their wants satisfied.

RE: Sprinklers in a library with minimal clearences

The only suggestion I would have is to treat the racks where the books are stacked as "walls." Can you just place sprinklers in the individual aisles? If possible, try to maintain a minimum of 6' between the branch lines so that if the books on the top shelves are removed, you don't have to be concerned with "cold soldering."

RE: Sprinklers in a library with minimal clearences

(OP)
There is an exception that has been used for this application to put the sprinklers in each aisle because of the clearance problem, but it refers to use with "racks" which is somewhat different than the "shelves" we will have.  I do not know if it will apply.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources