Steam Loss in Distribution Network.

Steam Loss in Distribution Network.

Steam Loss in Distribution Network.

(OP)
Hi all,

I am analyzing the steam loss in our steam distribution piping network.  I have looked into the metering loss, insulation loss and steam quality loss, but they contribute a very small amount in comparison to the total line loss.  Does anyone have any suggestions or ideas?

Thanks in advance.

RE: Steam Loss in Distribution Network.

Murphymok
Are you talking about pressure drops?  Steam loss due to condensation in the piping?  As in we produce 1000 kg/hr of steam and when you sum up the end users of steam we only get 500 kg/hr of useable steam.
If you could define the problem a little better we could help you more.

Regards

RE: Steam Loss in Distribution Network.

Only an idea: steam traps passing steam ?

RE: Steam Loss in Distribution Network.

Is your indication of flow element flow corrected for pressure + temperature correctly?

RE: Steam Loss in Distribution Network.

(OP)
Hi all,

We monitor the temperature and pressure closely and apply 0correction factors.  However, when I look at the steam sent out from the plants and the total sum measured at the customers, there is a huge steam loss, 10-15%.  We regularly check the distribution networks and manholes to ensure proper insulation and no leaks.  There are 3 losses I am thinking: condensate in piping, piping redundency and steam quality.  

Any suggestions will be greatly appreciated.

RE: Steam Loss in Distribution Network.

Is there any reason to suspect the customer's ethics? A slight modification to their flow element can result in a lower indicated flow than they are using. All it takes is an electric drill during a scheduled pipe shutdown.

RE: Steam Loss in Distribution Network.

There is no change is steam quality, it is all saturated isn't it?
The condensation is the big factor.  But "25362" had a good comment, bad traps.  A hand full of small vents 24/7 can sure add up to a lot of lost steam.
If you are looking for 10% you are getting down to the fine points.  I was expecting you to say that you were loosing 40%.

= = = = = = = = = = = = = = = = = = = =
Corrosion never sleeps, but it can be managed.
http://www.trenttube.com/Trent/tech_form.htm

RE: Steam Loss in Distribution Network.

I assume you will have a boiler feed tank or HOTWELL. This will have a vent to atmosphere which loses steam.
Flash steam from processes will also affect the condensate line pressure and the pressure/flash steam in the hotwell.

If you use flash steam recovery, this will reduce

go to SPIRAXSARCO.COM

Friar Tuck of Sherwood

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources