Differential current protection
2

Differential current protection

Differential current protection

(OP)
Hi, I´d like to know about the use of trafo´s for differential current protection, I´m working with a 6600 HP @ 6000KV AC 3 phase-60hz ring motor and it have one 100:5A trafo in each power supply line as a differential current protection, my question is, why I have to use this 100:5A trafo since the nominal current is arround 600A?

many thanks!

RE: Differential current protection

Are you asking why a ct is used as input to protective relays? Or why that ratio was selected?

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Differential current protection

(OP)
Exactly my question is about the reason to use a 100:5A trafo, and the conditions to actuate the protection

RE: Differential current protection

For differential protection the current getting into the motor stator is compared with the current exiting the stator. The very same Current Transformer (CT) will have the in and out lines of each phase (E.g. Motor lines #1 and #4). The result is zero current under normal condition. That is why your CT is rated 100 Amps and ratio 100:5 in spite of 600+ Amperes at full load. When an internal failure is developed into the stator windings, the currents in and out are different and the total current in the CT increases tripping the power supply.

RE: Differential current protection


Good info by aolade…  A couple of side notes are, 1) for a window CT, it’s important to keep the stator-coil external leads {1+4} routed symmetrically through the per-phase cores so currents cancel in normal operation.  [100:5 ratio provides significantly more current sensitivity than a pair of 600:5 CTs.]  

Note though, that differential-mode {87M} CTs are worthless for independently sensing motor running-overload [51/49] current, so can’t be applied in “all-in-one” motor protection.
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources