Damper activation requirments by the Fire Alarm Panel
Damper activation requirments by the Fire Alarm Panel
(OP)
Where can I find specific requirements for when Fire Alarm Panels need to tie to the Dampers? Thank you.
NFPA 90A and NFPA 72 (2002) 5.14.3.4
NFPA 90A and NFPA 72 (2002) 5.14.3.4





RE: Damper activation requirments by the Fire Alarm Panel
In the UK, smoke dampers in hospital theatres are deliberately NOT linked to the fire alarm system due to the danger of stopping the hygienic flow of purified air. The dampers in this case are manually operated by the fire brigade.
What application do you have in mind?
Friar Tuck of Sherwood