Can anyone tell me where the best sample point for hydrazine would be on a HRSG.  We had been sampling on the condensate, but I thought it would be better to sample on a drum.  Any other ideas.

RE: Hydrazine

The best place would be immediately upstream of the water feed into the drum.

If you sampled the drum water or downcomer liquid, it would not provide a true indication of oxygen ingress because the LP steam drum acts as a dearator, and strips the O2 off and the O2 passes out with the LP steam .

The steady state setpoint for O2 would be about 2-3 ppb O2, in order to avoid overfeed of hydrazine.

Most forms of hydrazine or carbohydrazide are n ot active until 300F, so any sample point upstream of the LP  preheater/economizer is useless.

RE: Hydrazine

(OP)
The sample point we have is downstream of our chemical addition, so if we are dosing hydrazine, we get erroneously high results.  It sounds like that is still the best sample point, but we need to get operators to pay attention to chemical adds.  Does that sound like a fair assessment?

RE: Hydrazine

Our cycle is: Condenser Pump - Heater 1, 2,3- Dearetor- Feed Water Pump -Heater 5, 6 , 7 - Boiler. Our inyection of hidrazine is regularly after the condensate pump (which is proportional to the condensate flow in auto), we check the concentration after the Dearetor and before the Boiler. We got some bad experience at begin, we preservate the boiler whit water with hidrazine at 170 ppm, but in the starts all the hidrazine desapear by the high temperature, at 315°C begins his descomposition resulting high values of hidrogen in the steam (experimental data). Actually we are controlling 25 ppb in feedwater before the boiler.

I hope that it can help you.

RE: Hydrazine

(OP)
Thank both of you for the help.  We do not have a deaerator, so your numbers may be different. We are supposed to maintain about 5-20 ppb residual, but I don't see the need if our oxygen level is within specification. Our only choices for sampling points are condensate, feed (after chemical addition), steams and drums.  It sounds to me like feedwater is the place to look.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources