Pfc and Ze - values by enquiry? (UK)

Pfc and Ze - values by enquiry? (UK)

Pfc and Ze - values by enquiry? (UK)

(OP)
Hi folks,
When installing a new board in a domestic situation, you have the option of aquiring the Prospective fualt current, and earth loop impedance values by enquiry.  Who do you contact to for these details?

RE: Pfc and Ze - values by enquiry? (UK)

Usually the REC responsible for the distribution network serving the premises will be able to provide this information. The values will be typicals, and they will almost certainly be conservative which leads you toward over-engineering your installation. Can't you hire a loop tester and get actual values? Or is this a new-build?




------------------------------

If we learn from our mistakes,
I'm getting a great education!

RE: Pfc and Ze - values by enquiry? (UK)

you need to measure pscc & earth loop on the various circuits after you have installed the board anyway so why not just measure them at the supply too

as scotty says, if you ask the LEB they will give you figures that are high and often by quite a lot. We recently asked for some figures and were told 16kA (P-P), when we measured it it was only 4kA (P-E so maybe 8kA P-P)

RE: Pfc and Ze - values by enquiry? (UK)

(OP)
Looks like i'll just have to take a couple extra readings, I just thought it could save a bit of hassle disconnecting the earth bound to measure Ze.

RE: Pfc and Ze - values by enquiry? (UK)

PhilT74

The REC always used to quote you 16KA (@ 0.55pf) as a maximum potential, this was assuming you were located next to thier transformer, as you found when you move away from the source and measured the reading it is significantly lower. Their figure is a distance of 35M for 4KA.

There are standard figures accepted and quoted for use typically 0.35 ohm for a TNCS - PME system, and 0.8 ohms for a TNS system as I recall. These can be used on your paperwork as the REC will quote these if you enquire. There is no substitute for a real test though.

Regards

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources