RTDs placement in stator winding

RTDs placement in stator winding

RTDs placement in stator winding

(OP)
Is it acceptable to put RTDs between top and bottom bars of different circuits of the same phase in a hydro electric generator? I am looking for the pros and cons of doing so in comparison to placing the RTDs in between the top and bottom bars of the same circuit of the same phase.

This is a six circuit generator i.e 2 circuits per phase.

All info is highly appreciated.

Thank you all.

Sarg

RE: RTDs placement in stator winding

Start by what can cause localized overheating?
A – Core problem
B – Cooling problem
C – Strand insulation breakdown / conductor eddy
D – Unbalanced voltage
E – Shorted stator turns????

I don’t see where A – C care about which circuit or phase is being monitored.  A and B only care about physical location.  

D will affect phases differently but affect all circuits within a phase the same.

So far no preference for same-circuit or different circuit.

The only mechanism I can begin to conceive of which might have preference for  one circuit over another is shorted stator turns.  But to it seems very unlikely this condition can exist for long without causing an electrical fault => not even worth considering for temperature monitoring.

Based on the above I don’t see any reason to prefer one over another.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: RTDs placement in stator winding

It is a good practice to distribute the RTD's circuit wise (to detect loss of a parallel circuit, which may not be necessarily picked up by differential protection unless it is specifically configured to cover all parallel circuits) as well as around the stator to get to an overall thermal map of the machine. Also, it is advisable not to place them near the cold air inlets for they are not hot spots.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources