Sizing Gas Piping

Sizing Gas Piping

Sizing Gas Piping

(OP)
I have a project which is using digestor gas (~60% methane) to run a generator which is listed as being used for this gas.  I have gas analysis so I know what the BTU/ft3 of the digestor gas.

I am responsible for sizing the piping to the generator.

I know how to size the piping if the gas is natural gas (~92% methane).

I have a general approach that I am comfortable will work but wanted to see if anybody has any actual experience with this.

RE: Sizing Gas Piping

I use to run generators on landfill gas @ 45-50% methane. It's all in the volume. The engine manufacture will tell you how many BTU's /min the engine requires. You size the supply system to feed the engine what it needs. Increase the volume in relation to the methane percentage. Use larger pipe or more compression to feed the lower BTU gas at a rate at which the engine will run.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources