Substitute CMU Block vs PIP

Substitute CMU Block vs PIP

Substitute CMU Block vs PIP

(OP)
Specifications for a single story warehouse foundation call for a PIP wall foundation (no change in footing) to a depth of 4' with #4 rebar lengthwise at 3' OC. The contractor has offered a reduced cost if concrete masonry unit (same thickness) is used. This appears to be OK for this application (building permit approved, I have authority to change). Should rebar be still be installed in CMU joint same as PIP or is no rebar OK? Lots of existing area foundations are without the rebar, but due to 40' span and 4" slab, the PIP was preferred.

RE: Substitute CMU Block vs PIP

The reinforcement requirements depends upon the combination of height of wall and the combined axial and wind loads (plus seismic where req'd).
A good rule of thumb for prelim is #5 bars at 48" vert and horiz.

RE: Substitute CMU Block vs PIP

CMU is an easy substitute, but review the circumstances with a local engineer. Minimal detailing recommendations should be observed. Many times, the steel is present only to control non-structural cracking. Your warehouse application sounds non-architecturally significant - meaning only that the likelihood of a lawsuit for non-structural cracks is not significant. The code allows unreinforced foundations, and they perform well within limits. Even these however should have control joints to control cracking. CMU with horizontal joint reinforcement performs well for minimal loading.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources