Motor lead splices

Motor lead splices

Motor lead splices

(OP)
I know that we have all tape-spliced motor leads in motor junction boxes, but I have never seen any written procedures for this process, i.e. what type of tape(s) to use, how many layers, etc.  These would be 50 - 200 HP AC motors, 1000 volt or 4000 volt.  The terminal boxes are rather small and the splices would have to be taped.  There is no room for the pre-formed splice boots.  Any help would be appreciated.
Thanks,
Podo

RE: Motor lead splices

My personal preferance is to use high press type lugs, bolted together with S/S bolts. One layer of good quality PVC tape to allow easy removal, 3 or 4 layers of linerless 44KV splicing tape. More layers the higher the voltage. Then cover with good quality cold weather electrical tape.

RE: Motor lead splices


Use of non-commodity-grade unshielded MV cable may be considered for controller-to-motor cabling to limit the increased volume generally required for shielded-cable installation.

I second AFab’s callout of seamless-copper-tubing tool-compressed lugs for compact and reliable connections.  Silicon-bronze hex-machine bolts with phosphor-bronze internal-star lockwaxhers are have a good track record.  

Various splitbolts or aluminum setscrew lugs with assorted junkbin hardware get used when nobody’s looking, until their failure blows holes in motor j-boxes.  For ANSI regions, tight quarters may be somewhat relieved with application of NEC 430-12 terminal-box sizing.

Suggested is the tried-and-true non-adhesive-backed varnished-cambric / linerless-rubber or silicone / 10-mil vinyl-tape finish.  (Cambric permits convenient “clamshell” stripping during teardown.)  in MV splicing, this method is sometimes refferred to as a built-up/field-fabricated
(compared to kit) application.  

Tape “insulation equivalent…” thickness implied by NEC 110-14 seems a bit vague and of marginal guidance.  Kerite has drawings of MV-unshielded splices, for they are a long-time major proponent of unshielded 5kV-class [NOT unishileded] materials.  Kerite prints are available through wwww.kerite.com/catalog/catalogfiles/terminating_splicing_power.htm

EPR/CSPE (or CPE) insulation/jacket flexibility {stranding aside} is typically more desirable versus XLPE/PVC versions.  The increased material cost is typically offset by reduced installation effort and increased long-term durability.  1kV circuits may be specified with 2kV unshielded EPR RHW-2 cable.  4kV circuits may be specified with 5kV unshielded EPR/CSPE MV90 or MV105 cable.
  
Minnesota Mining and Plymouth Rubber are two popular brands of insulating materials.
  

RE: Motor lead splices

3m makes high voltage splice kits for high voltage stress cones terminations, check with them.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources