On a self-contained liquid chiller system, I am specifying a combination filter/drier in the refrigerant circuit. With this in place, do I need to monitor the # of purge cycles in the control system as a secondary check, or is the purge method not used in the presence of a filter/drier?
TIA,
Brad
TIA,
Brad





RE: Chiller refrigerant purge question
If this is an absorption chiller, you could monitor the purge cycle with a PLC. If it's an electric vapour compression chiller you don't need to purge non-condensables from the refrigerant circuit.
Regards,
Cooky
RE: Chiller refrigerant purge question
Since 1990, all manufacturers of low-pressure chillers offer purges capable of operating when the chiller is idle or in standby. ASHRAE Guideline 3-1996 encourages designers to specify purges with "the capability of operating while the chiller is idle." Use of such purges can virtually eliminate refrigerant emissions caused by "air-bound" chillers and they come wth counters and alarms if too many purges are occuring.
RE: Chiller refrigerant purge question
http://www.trane.com/commercial/library/ashrae/en_27-02.pdf
which explains the ASHRE Guideline imok2 mentions. I think a purge system would only be necessary for a large chiller operating at low suction pressure, or if the chiller is likely to operate with suction pressures below atmospheric pressure.
Bleacher: If your chiller is operating at standard chilled water temperatures, I don't think you need the purge system.
Cooky
RE: Chiller refrigerant purge question
RE: Chiller refrigerant purge question
You can get them portable or for fixed install. Self installation is very simple and straight forward.
It's the same unit York sells for their chillers. Mine is 10 years old and has been very reliable.