MCC control room cooling
MCC control room cooling
(OP)
I am using a standard HVAC unit with air cooling a MCC room and the MCC control room controls a mfg operation with a lot of dust which is plugging the havac unit and it dies - what do I use in its place that can handle dirt.....?





RE: MCC control room cooling
Sure the outside exchanger foil is the dirted , specially as the air in a manufactruing room have oil minst.
I solve it attaching a simple air filter at the outside airs intakes.
If the intake air is small , expand it and put a proper filter.
Pardal
RE: MCC control room cooling
RE: MCC control room cooling
Other good way is to route freshair from a clean air place, it can be done from te roof or a near window.
If route is a long way , put a blade fan on the intake.
Other way could be to change the heat exchanger by a water cooled one, maybe there is a water cooling tower system piping.
Other is to split the HVAC equipment , and put the condenser on the roof , a fan shall be added.
Other is to change the HVAC by a split system.
I had handled about 260 units on a manufacturing plant.
It had filters , a nowoven fibers 25 mm thick.
What is manufacture at such plant???
Hope this helps tip , help you.
Pardal
RE: MCC control room cooling
RE: MCC control room cooling
which is the dust's origen.??
Pardal
RE: MCC control room cooling
RE: MCC control room cooling
pennpoint
RE: MCC control room cooling
RE: MCC control room cooling
Maybe its possible remote the condenser/condensing unit away from the MCC or the source of the dust.
Good Luck
pennpoint
RE: MCC control room cooling
RE: MCC control room cooling
As the condenser will be over the roof , if there is a leak , it will the same case when it is raining, and I guess you have not any problem when rains in your location.
Pardal