When the HVAC manufacturer's list MCA, minimum circuit amps, for a unit, does this number already include the 25% extra required by NEC for feeder sizing?

RE: MCA

Yes. It is included.

RE: MCA

(OP)
I do indeed, I like your answer.

RE: MCA

MCA does not necessarily include the full 25% markup on continuous load.  The manufacturer takes the evaporator fan, the condensor fan, and the compressor and adds them together.  They then add 25% for the largest motor of the group which is almost always the compressor.  This number is called the MCA.  So if you take the MCA and multiply by 80% you will not get the correct full load amps.

RE: MCA

Feeder motor loads only need to include 125% of the single largest motor supplied, not all MCA's. As mentioned in the previous post, 80% of MCA is not necessarily FLA.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources