According to the GAMBICA / REMA guide on best practice for the installation of Power Drive Systems (Guide 3). http://www.gambica.org.uk/

3.4.2.3 PROTECTIVE CONDUCTOR (EARTH) CONNECTION.

To operate as a protective conductor, the shield conductance must be at least 50% of
that of the phase conductor.

According to this SWA Conductivity Info:-

http://www.batt.co.uk/catalogs/industrial/Other%20Technical%20Information/247.pdf

All 3C XLPE BS5467 cables 6mm2 & above have a  Maximum armour conductivity expressed as a percentage (%) of one phase conductor less than 50%.

This means using 4 core cables from 6mm2 up to 16mm2 & 3 core with separate half size cpc for cables over 16mm2 (as advised by ABB).

What do others think about this?

Alan

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources