Cooling Tower plume formation

Cooling Tower plume formation

Cooling Tower plume formation

(OP)
Could someone, please, point me where I can find algorithm or formulas to calculated when and if future cooling tower would produce plume. Provided all ambient climatic conditions and cooling tower performance data are known factors.

RE: Cooling Tower plume formation


  IGORV2
         your Q is not clear are u talking about the Fan blades of cooling tower.

RE: Cooling Tower plume formation

If the available cooling tower latent heat rejection is less than the actual cooling tower heat rejection then the coling tower discharge air will be oversaturated resulting in fogging or plume.
That is if CFM x .69143 x (gr/lb humidity at saturation at ambient db - gr/lb humidity of ambient air) < Btuh heat rejection.

Where CFM = cooling tower fan CFM
gr/lb = grains per lb = 7000 x lb moisture/lb dry air

Btuh heat rejection = Cooling load Btu/hr + Compressor input in Btu/hr

RE: Cooling Tower plume formation

(OP)
pk786
It is fan blade Cooling Tower. Open cycle CW system for Co-Generation plant.
However I think lilliput1 has answered my question. I just have to convert it into metric system.
Thanks.

RE: Cooling Tower plume formation

There are two components of the visible mist off a cooling tower: drift as a result of entrainment of droplets, and plume as a result of condensation of the moisture of the outcoming air when in contact with colder air. These emissions are generally dealt with by installing mist eliminators and plume abatement (water pre-cooling) coils, respectively.

RE: Cooling Tower plume formation

(OP)
25632 Thanks.
I am interested in potential plume only. We believed we can eliminate drift with better then 0.001% drift eliminators provided by CT supplier.

RE: Cooling Tower plume formation

to igorv2, what CT cooling tonnage are you referring to when speaking of a drift as low as 0.001% = 10 ppm of the circulating cooling water, or is it the amount of particles on the atmosphere on the top of the CT ?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources