greetings...

   I would like to verify my interpretation of section 2304.4.1 of IBC 2002 stating that the capacities in table 2306.4.1 (allowable shear for wood structural panel shearwalls) are permitted to be increased by 40 % for wind design. Does it means  that sheathing with 15/32 in thk. ,10d nails spaced at 3" at panel edges and appropriate nails for intemediate member will now have a capacity of 931 lbs/ft instead of 665 lbs/ft?(supposing wind load governs in the design)
Im a bit confused because it is different on what is written in  UBC specifications. thank you...

RE: 40 % increase on wood structural panel shearwall

You are correct in your interpretation.  Allowable wind load values are 40% higher because the factor of safety for wind loads on shear walls and diaphragms is only 2, while it is 3 for seismic loads.

DaveAtkins

RE: 40 % increase on wood structural panel shearwall

Also, don't forget the seismic force calced is an ultimate force and the wind is an allowable.

To compare apples to apples, the seismic force is multiplied by .7 and then the shear wall tables may be used.  No increase for the seismic while wind may be increased by 1.4.

Makes a lateral design twice as long sometimes.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources