I am reviewing somebody else's design and I want just to be right in my decisin since I haven't work designing protections for at least 10 years. The situation is this:
I have a general protection specified as - 225AT - 225AF in a dedicated CB panel rated 225A-240V.
It feeds an MCC and one Light/Power panel (50A). the MCC feeds two pumps 1/2 HP each, one 40HP and a 15HP fans. The OCPD devices for the fans are 100A magnetic for the 15 and 175A thermomagnetic for the 40.

I have not found problems with the design but since I haven't done this in a while  iwant to confirm this is a valid design as per the NEC.

Thanks for your help

RE: sizing OCPD for HVAC fans

Suggestions marked ///\\\
I am reviewing somebody else's design and I want just to be right in my decisin since I haven't work designing protections for at least 10 years. The situation is this:
I have a general protection specified as - 225AT - 225AF in a dedicated CB panel rated 225A-240V.
///What is the 240V system, three phase or single phase three wire?\\\
It feeds an MCC
///What is the MCC bus rating?\\\
 and one Light/Power panel (50A). the MCC feeds two pumps 1/2 HP each, one 40HP and a 15HP fans.
 The OCPD devices for the fans are 100A magnetic for the 15 and 175A thermomagnetic for the 40.
///The sizes of protective devices suggest some form of the soft starting arrangement. If it is not the case, they will be needed for starting the 40HP motor. Definitely, 225A panel will not be able to support simultaneous DOL motor starts.\\\
I have not found problems with the design but since I haven't done this in a while  iwant to confirm this is a valid design as per the NEC.
///Please, notice that some manufacturers offer MCCs from 600A, 800A, etc.\\\
 

RE: sizing OCPD for HVAC fans

(OP)
Jbartos
thanks for your reply.
The system is a 240 3 phase. My thake is that the MCC bus should be at least 400A (in the design it is not specified).
What other  aspects of the design should I be aware of?

I really apreciate your help

RE: sizing OCPD for HVAC fans

Suggestion: If the process requires the simultaneous start of 15HP and 40HP motors, DOL, the service should be increased to 400A, 240V, 3-phase. However, the MCC come with 600A buses, normally. It can be made 400A by a main fusible switch or circuit breaker. Visit
http://www.directindustry.com
and search for Motor Control Center
which will return MCC manufacturers.
Also, visit
http://www.thomasregister.com
and type Centers: Motor Control under Product or Service, which will return 34 companies to approach to

RE: sizing OCPD for HVAC fans

(OP)
thanks a lot jbartos I will check those sites and check as per your recommendations
you have been very helpful

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources