Locked rotor time 4000V

Locked rotor time 4000V

Locked rotor time 4000V

(OP)
Hello to all,
I've been going through NEMA and IEEE standards trying to conclude the generally accepted minimum stall time for a 4000V, 3ph., 60HZ, 1250HP induction motor. NEMA specifies that that motors should be able to withstand locked rotor currents for at least 12 seconds. However, this only applies to motors rated at 500HP or less. IEEE 112-1996 specifies that the readings for the locked rotor test should be taken within 5 seconds after voltage is applied. Does anyone know of a standard or specification that might indicate the locked rotor time otherwise. Thank you all.

RE: Locked rotor time 4000V

Suggestion: Larger HP motors usually have their thermal damage curve available. Plotting the motor damage curve and the motor acceleration curve on the same I-t chart will reveal amount of time the motor can stay in the locked rotor mode (stalled) without being damaged.

RE: Locked rotor time 4000V

NEMA MG1 part 20, Large Induction Motors does not recommend a minimum allowable stall time, However it specifies the maximum value of load inertia constant ( W*k^2), reflected at the motor shaft, that the motor should accelerate at full voltage, assuming a load torque which varies proportional to the squared ratio of the speed and equals the full load torque at nominal speed.

RE: Locked rotor time 4000V

The motor should start twice if it is at room temperature, or once if it has the full load operating temperature.

RE: Locked rotor time 4000V

Comment: The motor can be designed for various starting duty. The motor manufacturer tech support should provide this information if it is not included on motor drawings or in the motor data sheet.

RE: Locked rotor time 4000V

(OP)
Thanks for your input,
     I agree that referencing to the thermal damage curve is the proper course of action regarding locked rotor times for large HP machines.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources