Does anyone know of any rule against running a propane line through an electrical room containing motor starters and/or switchgear? (Ontario)
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: propane line in MCC
Depending on how then line is constructed, it might change the area from unclssified to a classified area. Possible construction elements that would cause this is pipe joints, valves, connections etc.
RE: propane line in MCC
(1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through (d).
(a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
RE: propane line in MCC
RE: propane line in MCC
RE: propane line in MCC
I don't believe propane would trigger a hazardous classification. NFPA generally excludes propane and natural gas piping/valves/utilization equipment from triggering XP requirements -- that is, the gas piping to the gas stove in your kitchen doesn't mean you need XP outlets and lights. My understanding of the reasoning for this (I think it's in the NFPA footnotes) is that the burners on the equipment are a bigger hazard than the electrical installation, so if the burners haven't set off an explosion than neither will your electrical stuff.