Sound power limits for new large motors
(OP)
From reading the scope of NEMA MG-1 Part 9 we would conclude that it addresses motors up to 5000 hp:
“NEMA MG-1 2003
Section I GENERAL STANDARDS APPLYING TO ALL MACHINES
Part 9 ROTATING ELECTRICAL MACHINES—SOUND POWER LIMITS AND
MEASUREMENT PROCEDURES
SECTION 9.1 SCOPE
This Part specifies maximum no-load A-weighted sound power levels for factory acceptance testing of rotating electrical motors in accordance with this Standard and having the following characteristics:
a. motors with rated output from 0.5 HP through 5000 HP;
b. speed not greater than 3600 RPM;
c. 140 frame size and larger;
d. enclosures of the ODP, TEFC, or WPII type.”
However the associated tables 9-1 and 90-2 only address NEMA frame motors up to approx 500hp.
1 - Am I missing something in NEMA MG-1 which addresses sound requirements for large motors (as implied by the scope)? Or maybe it was a typo and 500 hp intended?
2 – What type of noise specification would you recommend for a new motor in an indoor machine-room environment – Power Plant Turbine Generator Building – hearing protection worn at all times.
“NEMA MG-1 2003
Section I GENERAL STANDARDS APPLYING TO ALL MACHINES
Part 9 ROTATING ELECTRICAL MACHINES—SOUND POWER LIMITS AND
MEASUREMENT PROCEDURES
SECTION 9.1 SCOPE
This Part specifies maximum no-load A-weighted sound power levels for factory acceptance testing of rotating electrical motors in accordance with this Standard and having the following characteristics:
a. motors with rated output from 0.5 HP through 5000 HP;
b. speed not greater than 3600 RPM;
c. 140 frame size and larger;
d. enclosures of the ODP, TEFC, or WPII type.”
However the associated tables 9-1 and 90-2 only address NEMA frame motors up to approx 500hp.
1 - Am I missing something in NEMA MG-1 which addresses sound requirements for large motors (as implied by the scope)? Or maybe it was a typo and 500 hp intended?
2 – What type of noise specification would you recommend for a new motor in an indoor machine-room environment – Power Plant Turbine Generator Building – hearing protection worn at all times.
=====================================
Eng-tips forums: The best place on the web for engineering discussions.





RE: Sound power limits for new large motors
http://www.reliance.com/mtr/pcno.htm
for Motor Noise issues. It can get involved if various regulations, e.g. OSHA, are to be complied with
Regarding NEMA MG-1 peculiarities, contact:
http://www.nema.org
for Errata, if any
and also, this topic may pose mechanical engineering challenges under Mechanical Engineers in this Forum
RE: Sound power limits for new large motors
I do not have MG1-2003 version,
NEMA MG1-1998 rev 2- 2001, part 9.6, 9.7 and table 9-1 limits the maximum Overall Sound Power level Decibels, (ref 10^-12 watts):
For 5000 HP, 1801 to3600 rpm; 114 – ODP, 120-TEFC, 109-WPII
For 4000 HP, 1201 to1800 rpm; 110 – ODP, 115-TEFC, 106-WPII
For 3500 HP, 901 to1200 rpm; 109 – ODP, 111-TEFC, 105-WPII