how does one calculate ierrupt current of a 200 A Panel which is connected to a 3000A transformer

RE: interrupt current

The primary factors are
- transformer voltage and kVA
- conductor size and distance to the panel
- possibly load contibution downstream

The basic answer can be had from a table. A more precise answer is obtained by a calculation method. Several other threads in this forum have contributions on this topic. Have you tried a search?

RE: interrupt current

If you are looking for the available short circuit current at a given point, you need to know what the available current from the utility is.  You also need to know the SC current available from the motors in the system.  

I suggest you use a good power system analysis program.

Wirenut

RE: interrupt current

Suggestion: Please, provide the following:
1. Transformer kVA
2. Transformer Voltage
3. Transformer Impedance
4. Transformer Short Circuit MVA, if known
5. Cable and or bus size
6. Cable and of bus length
7. If there is a reactor, then its parameters
8. Panel number of phases

RE: interrupt current

For a quick, dirty method, just divide the transformer rated full load in amps by the transformer impedance at that load, expressed as p.u., instead of percent.  The actual available fault will be somewhat less than this number because of the impedance of the source and low side conductors, etc.  But this gives you a number that lets you know if you need to do more study.  For your case, 3000 A divided by assumed 5% impedance gives 60,000 amps.  WOW!!

RE: interrupt current

For more quick and dirty methods, add up your motor full-load amps and multiply by 4 to estimate short-circuit contribution from motor sources.  This can be slightly refined by using 4.8 times FLA for motors 50 hp and above and 3.6 times FLA for motors smaller than 50 hp.

RE: interrupt current

(OP)
the short circuit rating of the transformer is 51700 A
the cable is 6-750 MCM
the length is 90 feet
what is the rating at the panel

RE: interrupt current

Suggestions:
1. Provide requested information. It is needed for obtaining correct results.
2. Unless you just keep yourself busy.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources