2MW Soft Start ??
2MW Soft Start ??
(OP)
Dose anyone Know if there is such a thing as a 2MW soft start .. it's for starting a compressor ... I am also looking into a VSD as well ...
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: 2MW Soft Start ??
RE: 2MW Soft Start ??
Check this link for one supplier (there are others): http://www.benshaw.com/index2.shtml
Try a Google search on Medium Voltage Solid State Starter
RE: 2MW Soft Start ??
Yes they are available, I have been involved in a couple at 440 volts, but in general, they would be at MV.
In addition to the links above, you could try http://www.aucom.co.nz
Best regards,
Mark Empson
http://www.lmphotonics.com
RE: 2MW Soft Start ??
There are a number of manufacturers of MV soft starters. In addition to the above you may want to try;
www.ab.com
www.solcon.co.il
There are a few more but their names/URL's escape me at the momment.
Regards,
GGOSS
RE: 2MW Soft Start ??
ABB
Siemens
Google picks 'em up alright.
-----------------------------------
Start each new day with a smile.
Get it over with.
RE: 2MW Soft Start ??
http://www.alstom.com
http://www.cegelec.com/
etc. for more info
RE: 2MW Soft Start ??
PS: jbartos,
I think you meant RFP. RFI would be Request for Information, a precursor to an RFP. Unless you meant Radio Frequency Interference, but I know not why you would!
"Venditori de oleum-vipera non vigere excordis populi"
RE: 2MW Soft Start ??
"Venditori de oleum-vipera non vigere excordis populi"
RE: 2MW Soft Start ??
RE: 2MW Soft Start ??
RE: 2MW Soft Start ??
I am interested in your comments re dv/dt problems with soft starters. Soft starters use SCRs which are very slow switching devices compared with IGBTs. I have not heard of any DV/DT problems with soft starters. Can you elaborate?
Best regards,
Mark Empson
http://www.lmphotonics.com
RE: 2MW Soft Start ??
Soft start is probably your best alternative. A VSD, variable speed drive, or variable frequency drive, VFD, is much more expensive in th medium to high voltage. The advanage of the VFD is the ability to save energy on variable torque loads, fans and pumps typically. An energy savings come at a large price in the medium voltage arena. Voltage and FLA of the motor are the key to sizing this unit. I suggest contacting the following web site www.benshaw.com
Patrick
RE: 2MW Soft Start ??
I agree with you this places a lot less stress on insulation systems but in a proposition such as the 2 MW machine (which I assume is not young) it should not be ignored. Some soft-starter manufacturers make reference to the dV/dt filters installed in their equipment.
My first VSD installation was to retro-fit an SCR-SCR type in the mid-seventies and within 18 hours precipitated a winding-to earth fault in a long-dormant insulation weakness in the rather older motor it supplied. I've had NO motor failures attributable to soft starters or VSD's since but only three of my direct projects have included soft starters in LV works. ... I've also been a lot more cautious.
RE: 2MW Soft Start ??
Thanks for your reply.
The switching times with IGBTs are in the order of hundreds of nanoseconds, and as you suggest, these wavefronts are occuring at a very rapid rate, typically 5 - 15 KHz. I believe that the greatest problem is not from the switch ON, but from the switch OFF.
In the case of SCRs, the switch ON time can be in the order of microseconds to tens of microseconds, and the switch OFF more in the order of tens of microseconds to hundreds of microseconds. Switch OFF occurs when there is no curent flow, so there are no steep fronts at that point.
The switch ON is probably more gentle than a contactor closing, the only problem is that this occurs every half cycle during start.
I have not experienced any dv/dt failures that can be directly attributed to soft starters, and I have been involved with many tens of thousands of installations over more than twenty years. I would suggest that the potential for dv/dt damage is probably no worse than electromechanical switching.
Best regards,
Mark Empson
http://www.lmphotonics.com
RE: 2MW Soft Start ??
There are two windings, main and the feedback winding on the same magnetic core.The soft starter offers a high impedence when the motor is startted.As the motor speed increases the emf to the feedback winding increases and the effective impedence decreases. The motor starts very smoothly.The soft starter is removed fron the circuit after the motor starts.
No harmonic problems!!!!