Circuit Breakers with different short circuit ratings
I would like to know if anybody has used circuit breakers in a power distribution circuit where the upstream circuit breaker and the downstream circuit breaker ( maybe incomer to another distribution board) have different short circuit ratings. There is no fuse used anywhere in the circuit.
RE: Circuit Breakers with different short circuit ratings
Mike
If there is no impedance in between the two breakers,the downstream device can be series rated as per manufacturer specs and testing. This has been discussed in this forum previously...maybe try keywords "series rated"??.
Should have used keyword search. It is available in :
http://www.eng-tips.com/viewthread.cfm?SQID=21916&SPID=238&newpid=238&page=3
Now I want to know if anybody has used series rating/ Cascading applications with selective discrimination in any of your industry. I have read some literature but would like to know if it has been carried out in real life situations especially in three phase power distribution schemes. I know it is being done for lighting .
Dandel
I would also like to know as to how you think it is possible. Have you seen it anywhere. I do not want to take the cable impedence or the presence of a fuse in the scenario to reduce short circuit levels.
Thanks to all
If you use U/L labled molded case breakers check out what the interrupting rating really means. The U/L test method calls for about 10 feet of wire on the load side of the breaker during the test. The wire used will be the maximum size permitted for the breaker size. On the smaller breakers the 10 feet is sufficient to cut the fault from about 35kA down to 14kA. The breaker will be approved for use with a 35kA source. If you should happen to short wires while working near the breaker terminals it will probably not clear the fault. We found this out the hard way. This was a topic of interest in a past IEEE PCIC and IEEE IAS conferences where some folks tested this and photographed the results as part flew out of an open MCC bucket. Wire impedance can be significant.
Yes, discrimination is applied on almost all circuits, regardless of their purpose. It has to be, otherwise a fault on a small circuit would trip everything back to the utility transformer, if not back to the generating plant. This is achieved by discrimination on either a time or current basis on most LV systems. In addition to discrimation techniques, more specialised protection schemes are found on MV and HV systems and heavy-current LV systems, by restricting the zone over which the protection operates, or by making the protection sensitive to power flow in a certain direction, and so on. That is probably getting a bit too complex for this discussion, but protection is a fascinating field.
The use of cable impedance or transformer impedance to limit fault levels is standard practice. Fault level limitation by cable impedance is usually a fortunate result of using real-world cable sizes to supply real-world loads, where cable size is usually based on current-carrying capacity. Occasionally it is necessary to increase a cable to a larger size to withstand fault current, but while this is a prudent check for any design, the situation doesn't arise that often.
Transformers are deliberately designed with an impedance which restricts the prospective fault to a level which switchgear is cable of clearing. It is possible to design transformers with very low impedance, but switchgear becomes difficult to obtain or has to be designed for the application. In most situations the degradation in transformer regulation from no-load to full-load caused by increasing the transformer impedance slightly is of little or no consequence, while the benefits of limiting the fault level are apparent in reduction of conductor and switchgear size and cost.
Start each new day with a smile.
Get it over with.
Have you tried bussman's library for more info?
http://www.bussman.com/apen/pubs/
or directly for series rating...
http://www.bussman.com/library/docs/series%20rating%20SPD.pdf
In my 30 plus years of experience, most as a service engineer, I have not seen a single ciruit breaker failure that could be attributed to the fact it was not rated for the available fault duty and the upstream fully rated breaker failed to clear.
Series-rated systems are based on an upstream device opening for a fault before the maximum fault current is reached. This technique can be used to 'limit' the fault current at a lower-rated downstream device, but it will only accomplish this by opening under the fault, which removes the selective coordination from the system(discrimination).
For instance, you may have a 400A fuse open the feeder to a 400A panel when the fault was on the load side of a 20A feeder C/B in the 400A panel. If the system was fully-rated, the 20A C/B would be designed to open and isolate the fault from the rest of the system. In a series-rated system, the whole 400A panel is de-energized.
///Often, the power distribution system physical geometry covering length between different panels, power distribution panels, switchboards, switchgear is such that one level downstream circuit breakers and buses (panelboards, MCC, switchboards, etc.) have lower short circuit level rating. If the buses are were close, then the short circuit rating will be necessary to be the same. The short circuit rating is a safety related since the protector may explode. It is somewhat different from the selective coordination since the protectors may have the good selective coordination and be improperly rated short circuit-wise thus causing a potential hazard. This area is often very poorly understood and in some instance poorly engineered and designed.
Nowadays, any more important or noticeable size electrical power distribution system is modeled by suitable software before it is constructed. The software normally includes short circuit and voltage drop analysis programs, e.g. SKM, Inc. DAPPER, A_FAULT, etc.\\\
///Good to know.\\\
Or have you seen a power distribution circuit where the upstream circuit breaker is from a MCC/PMCC and feeds another distribution board which has outgoing breakers having lower short circuit ratings.
///Yes, this is quite normal if the distribution feeder is sufficiently long, i.e. has an adequate impedance to reduce the short circuit current (fault) down to the next standard interrupting rating level of a circuit breaker and its panelboard, switchboard, cabinet, etc.\\\
There is again no fuse used anywhere in the circuit.
PWR-It is a relief to know that this technology is being used somewhere in this world.With such an experience I would certainly like to consult you before pushing this application in my projects. Could you send me your email address at pandeys@mantraonline.com
Dandel- Your reply is very appropriate. I would like to add my views about my favorite topic IEC vs NEC. What I could gather that in the NEC world Series rating tests conducted by UL is such that panelboards/distribution boards are certified if both the incoming and the outgoing breaker trips on a short circuit in the outgoing feeder. However as you mention this can break power supply to the entire panel which has several outgoing feeders.In the IEC applications where UL listing is not required , supplier have started to gaurantee selective discrimination along with the series rating (also known as cascading).
jbartos- You certainly have a good view of the present philosophy that we engineers follow. Hoever I would like to bring about some change with increasing technological developments . Only one thing struck me. Why do you say that it is good to know that no fuse is being used?
Thanks again.
uno
http://www.eatonelectrical.com/unsecure/cms1/PU08703002E.PDF
http://www.eatonelectrical.com/unsecure/cms1/1C96944H02F.PDF
IEC cascade rating-
http://www.eatonelectrical.com/unsecure/cms1/IA01217001E.PDF
In your 4/29 post you state/imply that fully rated and selectively coordinated might be related. This is not at all true. What could be true is that a selectively coordinated system is fully rated, but the converse is not true. There are a number of examples where one can have both a fully rated combination of two breakers and a series rated combination where the manufacturer's trip curves are identical between the two. I could even put together the same thing using a fuse and a breaker.
Where did I say that all fully-rated systems are inherently coordinated, as you imply?
///A fuse can be current limiting. Such fuse can reduce the short circuit current, e.g. from 100,000A to about 15,000A (see Ferraz-Shawmut fuse AD2 or AD6). If such a fuse is prudently engineered and designed in the power distribution system, it will significantly reduce the short circuit current level downstream. Consequently, the downstream circuit breaker short circuit interrupting rating will be much lower, and so will be bracing of buses in panelboards, MCCs, switchboards, switchgear, etc.\\\
In your 4/29 post you stated "If the system was fully-rated, the 20A C/B would be designed to open and isolate the fault from the rest of the system. In a series-rated system, the whole 400A panel is de-energized."
It would take a fully rated system to in fact to that, but fully rated is not a sufficient condition. There can be many fully rated systems where the 20A and the 400A would race each other for fault currents in excess of 4000-8000A. In fact, to achieve a selectively coordinated combination of a 20A breaker and a 400A breaker you will most likely need to use an electronic trip on the 400A breaker that allows you to turn off the INST trip element of the 400A breaker; or somehow limit the fault current at the 20A breaker to less than the INST pickup of the 400A breaker.
I have run into a number of clients who think that fully rated sounds better than series rated and they insist on fully rated simply because in series rated the upstream device is required to trip to help the downstream device clear the fault. This is not a reason to decide between series rated and fully rated; there are other legitimate reasons to pick fully rated over series rated, and cases where series rated is not allowable (motor contribution between the upstream and downstream devices), but selectivity cannot be achieved simply by requiring all devices be fully rated.
The upstream MCCB (or fuse) / downstream MCCB combination is chosen from MCCB manufacturer's certified tables.
This ensures that in the event of a fault on the load side of the downstream MCCB, the upstream MCCB limits its let-thru current to below the interrupt rating of the downstream MCCB.
Note: Manufacturer's of current limiting MCCBs publish curves showing MCCB let-thru current versus prospective current. This reduced let-thru current can not be used to specify the required interrupt rating of a downstream MCCB.
This is because the tests are done with the MCCB load-side terminals shorted by a prescribed cable size/length.
When two MCCBs are in series, the let-thru current is different and can only be determined by tests.
'Cascading' is when both MCCBs in series trip for a fault on the loadside of the downstream MCCB. The upstream MCCB limits the let-thru current to below the interrupt rating of the downstream MCCB.
'Cascading' and discrimination is now possible.
See www.schneider-electric.com/cahier_technique/en/home_en.htm
"Interplay of Energies in Circuit Breaker and Fuse Combinations" IEEE Transactions on Industry Applications, VOL 29, No. 3, May/June 1993.
I believe that the main disadvantage of a series-rated system is loss of selectivity, and so do many people who are responsible for industrial power systems. The loss of one small circuit is very often significantly more preferable economically to a larger outage that could have been prevented by the proper design of an electrical system, which, in my opinion, would start with fully-rated devices.
You may have other priorities and experiences, and that's fine; I understand what you are saying.
I agree 100% that a selectively coordinated system will be fully rated, and that a selectively coordinated system can be highly desirable. What I disagree with is the implication I read in your post (whether it existed in your mind or not) and have read many other places, is that since series rating means both devices trip, fully rated means that only the down stream trips. The implication seems to be that series rated vs. fully rated is a binary choice. There are really three choices: series rated, fully rated (but not selectively coordinated), and selectively coordinated (which is inherently fully rated).
Selectively coordinated is highly desirable in many instances, and can be a great deal of fun design, but can also be extremely expensive to implement for smaller circuits or for systems with several overcurrent devices between a significant transformer and the final load. To do selectively coordinated at low voltage with circuit breakers usually requires solid state trip units with the ability to turn the INST trip off or set it above the available fault current.
I think we agree more than we disagree, but could we agree that "fully rated" covers too much ground to be used without further qualification regarding selectivity?
Your statement is true up to a certain point, but most CBs have a high-set function for which the tripping time is not clearly defined. A heavy fault may well cause the high-set function of both the upstream and downstream CBs to operate, giving a 'race' condition where both CBs see the fault and react to it by initiating a trip. The high-set function is 'instantaneous' in so far as real world apparatus ever can be instantaneous, and this makes grading between devices impossible unless the downstream high-set level can be set to a level which allows the downstream CB to clear a fault while the upstream CB is on the I-t curve. Some of the larger and more expensive CBs allow the high-set to be turned off, which makes this possible.
I thought the US used standard curves - ANSI? - for the responses of protection relays. Does this apply to breakers as well? In IEC land, we find it easy to grade CBs from different manufacturers because they all conform to standard curves defined in BS7671 as Types B, C, & D up to a certain size. Larger breakers have their own means of 'bending' their response curve to suit the application, rather than a set of pre-defined curves. HV curves are defined in a standard whose number eludes me but are known as: EI - extremely inverse; VI - very inverse; SI - stanadrd inverse.
Get it over with.
A full function electronic trip unit will have adjustable long time pickup, long time delay, short time pickup, short time delay, instanteous pickup and earth fault pickup and delay. Some curves can be definite time or I^2t. Various combinations of functions and ranges of settings are available. In the ANSI regions, elimination of instantaneous or hi-set function is allowed only on ANSI standard power circuit breakers (ACB's) installed in ANSI standard low voltage switchgear.
Your statement "In the ANSI regions, elimination of instantaneous or hi-set function is allowed only on ANSI standard power circuit breakers (ACB's) installed in ANSI standard low voltage switchgear." was more definitive a few years ago than it is now. With going to ANSI type gear, you can use the new Square D (MG) Masterpact and Cutler-Hammer Magnum DS breakers as UL insulated case breakers with the same set of trip functions as are available when used as ANSI LVPCBs. The breakers have a fixed INST override function set at their short time rating, but if the breaker is selected such that the maximum available fault current is below the short time rating, the tripping will be the same for UL and ANSI.
See also Thread238-78317
Hi jB,
///Yes, below .o1 sec. Such devices can only be coordinated on enegetical basis needed for tripping, if electromagnetic and if electronic, then there is the short-time delay setting of upstream breaker serving as a backup of the downstream instantaneous setting of breaker or protecting cable between load side of upstream breaker to the line side of downstream breaker(s).\\\
///Yes, this is true for the circuit breakers that have no electronic trip unit, e.g. GE MicroVersaTrip, Square D Micrologic, Cutler-Hammer Digitrip, Siemens SensiTrip, etc. and those electromechanical breakers that have the same t*I*I peak through.\\\
///Yes, this is still possible to see, engineer and design. However, the technology is there to avoid it. I always try to avoid it (even if it costs more money).\\\
///Nowadays, even the small CB three phase circuit breaker from about 3A up, see GE site for breakers.\\\
///Yes, mostly for electromechanic and solid state. However, the integrated digital relays do seem to have various algorithms and logic for the more sophisticated protection.\\\
///The electronic trip units marketed worldwide, e.g. Schneider Electric / Square D do use the long time setting, long time delay, short time setting, short time delay, ground fault, t*I*I, and instantaneous setting.\\\
As far as I know, your understanding is correct. If one selects the UL 489 version such that the short time withstand rating (same as the INST override setting) is above the maximum fault current, the trip characteristics are the same as the UL 1066 (ANSI) versions. Without digging out the material, I believe that the UL 1066 versions also have INST overrides, but for that application the breaker AIC rating is the short time rating.