Hi

To convert a 60Hz genset to 50Hz, we need to slow the diesel engine and reduce the excitation (Drop the output voltage)

While I have done this on medium sized machines with no difficulty, are there any problems doing this on large machines? the suggestion from the manufacturer is that the injectors and supercharger would need to be replaced.

I am interested in your comments.

Best regards,

Mark Empson
http://www.lmphotonics.com

RE: 60Hz to 50Hz generator conversion

I assume that the optimum power output and efficiency of an engine is designed for the nominal speed. As any motor when the speed drops, the power output drops proportional to the speed assuming that the torque produced is constant.

May be a Mechanical Engineering Forum could give a more accurate answer.

In regard to the generator, if the speed is reduced, the generated voltage will be reduced too, ( e=-NKdF/dt, were N is the series turns and dF/dt the flux rate change).

If the excitation is kept constant, the voltage will drop proportional to the speed (83.3% of that at 60 HZ).

As a result the generator Power is reduced too. If the excitation is increased as compared to that for 60HZ, the magnetic circuit could be saturated, overheating the field and the exciter. Another factor is the cooling fans, with  reduced speed they will provide lower cooling air.

As a resume, a 60 HZ generator could work at 50 HZ but with reduced power and voltage. If the excitation is reduced the drop in power is more significant, following the voltage drop.

RE: 60Hz to 50Hz generator conversion

Suggestion: Visit
http://www.kohlerpowersystems.com/pdf/G5236.PDF
and compare parameters for 60Hz and 50Hz at 220V/380V
e.g.
             50Hz             60Hz                50Hz/60Hz=0.83
kW         1760              2000               1760kW/2000kW=0.88
kVA        2200              2500               2200kVA/2500kVA=0.88
Amps      3798              3343               3343A/3798A=0.88
RPM        50                  60                 50RPM/60RPM=0.83
Etc.

      

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources