Getting online with SLC 5/05 using PIC driver

Getting online with SLC 5/05 using PIC driver

Getting online with SLC 5/05 using PIC driver

(OP)
I have a tool that we want to put on the plant network.  I look at the I/P address offline, it conforms to our spec so I believe it to be the correct I/P address for that processor.  I cannot ping it so I need to go online through the DF1 port, which is configured to communicate with a Panelview.  According to AB if I use the 1747-PIC driver I should be able to comm through the DF1 port.  I have set up RSLinx to run as a normal application.  Can anyone offer any suggestions?

Thanks.

RE: Getting online with SLC 5/05 using PIC driver

Hello;
     You need to find out how the serial port is configured on the processor. Possible options and to cooresponding RsLinx drivers are:

DH485                       RS-232 DF1 Devices
DF1 Full Duplex             RS-232 DF1 devices
DF1 Half Duplex Slave       DF1 Polling Master
DF1 Half Duplex Master      Not possible
DF1 Radio Modem             RS-232 DF1 Devices?
Shutdown                    Not Possible

RE: Getting online with SLC 5/05 using PIC driver

Set up DF1 driver in Linx, then you will need a 9-pin to 9-pin serial lead (AB will sell you one 1747-CP3, but it's only as detailed below).

2-----3
3-----2
5-----5

Hope this helps.

RE: Getting online with SLC 5/05 using PIC driver

Add to jamspop:
you may need to connect on both connectors

7 --- 8  and  1 --- 4 ---6 , too.

<nbucska@pcperipherals.com>

RE: Getting online with SLC 5/05 using PIC driver

If you are setting RSlinx to use the 1747-PIC driver then  
under Channel configuration on the SLC5/05  the channel 0 - system setting must be set to DH485, baud rate will automatically be set to 19200 and set the appropriate node address. Under General the Channel 0 mode must be set to System, user driver is normally set to shutdown.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources