Getting online with SLC 5/05 using PIC driver
I have a tool that we want to put on the plant network. I look at the I/P address offline, it conforms to our spec so I believe it to be the correct I/P address for that processor. I cannot ping it so I need to go online through the DF1 port, which is configured to communicate with a Panelview. According to AB if I use the 1747-PIC driver I should be able to comm through the DF1 port. I have set up RSLinx to run as a normal application. Can anyone offer any suggestions?
Thanks.
Thanks.
RE: Getting online with SLC 5/05 using PIC driver
You need to find out how the serial port is configured on the processor. Possible options and to cooresponding RsLinx drivers are:
DH485 RS-232 DF1 Devices
DF1 Full Duplex RS-232 DF1 devices
DF1 Half Duplex Slave DF1 Polling Master
DF1 Half Duplex Master Not possible
DF1 Radio Modem RS-232 DF1 Devices?
Shutdown Not Possible
2-----3
3-----2
5-----5
Hope this helps.
you may need to connect on both connectors
7 --- 8 and 1 --- 4 ---6 , too.
<nbucska@pcperipherals.com>
under Channel configuration on the SLC5/05 the channel 0 - system setting must be set to DH485, baud rate will automatically be set to 19200 and set the appropriate node address. Under General the Channel 0 mode must be set to System, user driver is normally set to shutdown.