Heat exchanger tube cleanliness factor
I'm preparing a specification for district heating heat exchanger. We are thinking to use Stainless steel for tubing but we will not provide tube cleaning system. The water temperature can vary from 50-105C. Water quality seems to be OK, specific conductivity 220 MicroS/cm,PH 9,TDS 220 mg/l,calcium 0.8 mg/l, chloride 8mg/l,dissolved oxygen 10 mg/l, sulfate 36 mg/l.
Does anyone know what would be the best cleanliness factor for this tubing? Would 90% factor be appropriate? In this heat exchanger if we do not have tubing cleaning system, will chemical cleaning be appropriate? Any drawback?
Thank you in advance
RE: Heat exchanger tube cleanliness factor
I'm assuming you're looking at a water to water system. The district side of the HX will be (better be...), as should the customer side, be tight, and leak free. The big killer of closed-loop hot water heating systems is make-up water, due to leaks. Leaks can include losses through relief valves due to improperly selected and installed expansion tanks.
The main problem I've encountered with district heating system HXs, is where there are chronic leaks on the closed loop water side of a steam-to-water arrangement. The continuous trickle of oxygen-filled make-up water has corroded the system to the point where the HX (in the basement) routinely plugs with black goo. I've told them that this muck is actually the inside of their heating system, and that they've absolutely got to fix the leaks and flush the system, but the shop has been downsized to the point that there's not even enough bodies left to fight fires, let alone get ahead of problems like this.
If there's glycol in one or both loops, then it must be chemically checked annually. Glycol can break-down into some interesting acids, and really go after your system.
If the HX is for domestic hot water, deposits will typically be from hard water. This will happen no matter what kind of system you use. Install pressure gauges and inlet/outlet thermometers across the DHW side (this should be done on any HX to troubleshoot and monitor it), and get base-line readings on a new, clean HX. Someone must check the installation periodically (don't laugh - it happens sometimes) and when the delta-P drifts up, it's time to pull the HX out of service, and clean it.
If it's a district steam system, really the only way you can get deposits on the steam side is if there's serious carry-over back at the boilers.
90% cleanliness factor is recognized as OK for hard metals such as various SS alloys, as opposed to 85% for soft metals like brass and CU/NI.
The presence of chlorides to any extent concerns me.  As a rule of thumb, 300 series SS does not like chlorides, but might tolerate up to maybe 100 ppm, depending on other factors.
Go to; http://www.trenttube.com/Trent/technical_assistance.htm
and ask them to e mail you a copy of:
Selecting Tubing Materials for
Power Generation Heat Exchangers
(by)
Daniel S. Janikowski
General Manager – Power Tubing
Trent Tube
2015 Energy Drive
East Troy, WI  53120
This is one of the best papers I have seen as far as having a comprehensive side by side comparison of a large variety of tubing metallurgies for heat transfer situations.  They have data for brass, copper alloys, austenitic and ferritic SS alloys, Duplex alloys, as well as theirs and others super ferritics.
The answer to your 90% question is also in there, as well as others that you asked.
regards,
rmw