motor overload tripping classes eg class 10,15,20
Can anyone give me definitions &/or explain the difference between the different motor overload tripping classes, eg class 10,15,20 etc. As described in overload manufacturers specifications.
Any help greatly appreciated,
Justin
RE: motor overload tripping classes eg class 10,15,20
An overload-relay class number indicates the maximum number of seconds at which it will trip when carrying 600% of its rating.
phasey,
The tripping curves actually have at least 3 detemining points, I believe at 1x FLA, 2x FLA and 6x FLA. It is only the 6x number that is used to classify the curve for simplicity. It is also important to understand that the curve class is based on a MAXIMUM tripping times, but protection devices can pass if they trip sooner. This can of course mean that nuisance tripping may occur, and frequently does with cheap overload devices. Also,
"Venditori de oleum-vipera non vigere excordis populi"
Hello phasey,
There is an FAQ on this subject in the FAQ section if you are interested. There is also a very good discussion thread at www.lmphotonics.com/forum
I hope these will answer any questions you may have on the subject.
GGOSS
Comment: The intent of the thermal overload is to have its I-t characteristic close to the motor starting characteristic and as far as possible from the motor thermal durve. Therefore, different classes have been developed to protect the motor sensitively.
Keep in mind that overloads can not trip too quick because they are not for short circuit protection so there is a bottom limit to the trip time as well. Otherwise, they can trip sooner than the trip class rating as pointed out.
Comment. The overload protection is not exactly accurate protection considering the overload sensors (heaters) principles of operation. That is why there are so many malfunctions happening in areas of the motor overload sensing and relay protection.
The old thermal OL were not that accurate (not ambient temp compensated) but the new ones are improved. There are many micro based relays that are definately accurate. You will get what you pay for in this area.
Amplifying buzzp's point, we have had excellent results using Sprecher & Shuh solid state O/L's.   Our applications are chiefly on rotary electric vibrators, which are quite prone to O/L events, due to frequent borderline abuse operation.   We also have saved a few compressor motors by using these, also a tough app.
BK
Jbartos,
 I am not sure what those two links are showing us or telling us. The solid state relays are very accurate devices assuming a sinusoidal waveform. However, there accuracy may worsen if your talking about hacked up waveforms or distorted waveforms. This is because they generally operate assuming a pure sine wave and use the averaging of peak detection to come up with the rms value of current. They generally do not respond to the real rms current such as a temperature operated OL. I am sure there are some that actually have an rms responding circuit but not many. So yes, in the case of distorted waveforms, solid states do suffer some accuracy, in general. But not always.
We are right now finalizing the design for production on a new SSOL (which by the way will do exactly what the OP wants) so I can speak directly to the accuracy issue. When duplicating the functionality of a bimetal OLR, we took measurements of many manufacturers' units in operation, finding the inacuracy to be astounding, i.e. as high as +- 20% in some. Fortunately the only thing relatively consistent was the fact that they rarely exceeded the maximum trip time for their class. Most tripped earlier and many would even come under the heading "nuisance" if you asked me. Still, better safe than sorry.
In the SSOL world, accuracy is dead on perfect as far as the digital processes go. When the algorithm says to trip at a particular level in a set time, it does it. The inaccuracy in the system comes from the input measurement method and the sampling rate. We are using 2% class CTs in ours so there is at least a +- 2% risk there. We have played with the sampling rate a bit and found that beyond a certain level, easily atainable by even the lowest cost components, there is no significant loss of accuracy. So even the cheapest of SSOLs should be more accurate that the majority of bimetals. Of course anyone can make crap, but without an economic incentive to do so, why would they make the sizeable investment in bringing a product like that to market?
For buzzp, you are dead on about the distorted waveforms. A version for use behind VFDs will use Hall Effect transducers and I have yet to see accuracy results on those, but I am told they will be similar. The sampling gets real tricky though and we need to use a comparatively high rate to avoid adding error. That version is still in the skunkworks.
Oops, the "OP" referred to was in a different post, Thread237-93739. I got them mixed up
Comment: The only thing that is puzzling when there is such an impressive accuracy available, why is it that it is not mentioned upfront in the literature?
In general, I have found that if no easily obtainable accuracy specs are available then the device is probably not worth buying.
Jraef, is your new SSOL using a RMS method or are you calculating this based on the peak or average value? Just curious. As far as the VFD OL's, I have heard (not confirmed nor tested nor thought about much) that depending on the CT and the carrier frequency of the drive, the waveform that comes out of the CT would already be filtered (smoothed) enough to not require any special sensors (hall effects or other). Since the motor smooths out the same signal, then the argument is no special sensor is required. It looks as though you work for a drive manufacturer. I would be interested to hear if the above statements hold water compared with any testing you have done. What methods do you use, presently, to measure the current out of the drive? Thanks.
Thank you all for your help much appreciated.
justin
