(OP)
I have a battery room that houses 53 lead acid cells of 2.2Vper cell and 214 amp-hour. I would like to know if this installation must be considered an Hazardous Location. What constitutes an hazardous location?

Thanks

RE: Hazardous Location

Any flamable vapours or gas is Class 1 Div 1 and must be installed by your applicable codes

RE: Hazardous Location

Comment: The release of hydrogen from lead acid can cause an explosion if a certain concentration materializes. Therefore, reliable ventilation is required. In some cases, the battery room large openings or large open windows may suffice. The calculation of the hydrogen concentration should be performed.
IEEE Std 484 in 5.1.4 Ventilation states "The battery area shall be ventilated, either by a natural or induced ventilation system, to prevent accumulation of hydrogen and to maintain designed temperature. ..."

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources