Does any one know how to calculate generator I2^2 t curve for coordination purposes?
I know that K varies between 2 - 40 and I2 is percent of stator FLA. What percent of FLA is used to draw the curve?
Hope the question makes sense.
Thanks in advance
I know that K varies between 2 - 40 and I2 is percent of stator FLA. What percent of FLA is used to draw the curve?
Hope the question makes sense.
Thanks in advance






RE: Generator Negative Sequence Protection
RE: Generator Negative Sequence Protection
The ability of a generator to accommodate unbalanced currents is specified by ANSI C50.12 and ANSI C50.13 in terms of negative-sequence current (I2). IEEE C37.102 specifies the continuous I2 capability of a generator and the short time capability of a generator, specified in terms I22t and defined in a dual-slope relationship plotted against generator MVA.
RE: Generator Negative Sequence Protection
http://pm.geindustrial.com/FAQ/Documents/SGC/GER-3181.pdf
http://www.abbus.com/abbrelays/pdf/100/41_178s.pdf
for
etc. for more info
I2^2xt may be given or measured.