Distribution of horizontal shear stree by BS8110, cl.5.4.7.2.
Anyone can show me how?
The clause said that the average horizontal shear reinforcement should be distributed in proportion to the vertical design shear force diagram to give the horizontal shear stress at any point along the length of the member. But how?
Finding the average vertical shear force and then distributed it by ratio? or other method?
Please help
Please help
RE: Distribution of horizontal shear stree by BS8110, cl.5.4.7.2.
prex
motori@xcalcsREMOVE.com
http://www.xcalcs.com
Online tools for structural design
links provide shear resistance acting in tension to hold back the diagonal shear crack in a beam in flexure.
your horizontal shear can be taken care by shear studs if you say casting a composite steel-concrete deck. then u have to know the shear stress at the interface
Carl Bauer
www.bauerconsultbotswana.com
I have checked BS5400, cl 7.4.2.3 and BS8110, 5.4.7. They are suggesting different methods for estimating the horizontal or interface shear stress. BS5400 sugguest using v=VQ/IB ( which is the exact shear stress at the point being considered ), while BS8110 sugguest to find the average horizontal shear first ( C= M/Z , C/bd ,C-compression ) and then distribute it in proportional to the vertical shear diagram. I feel it is quite hard to understand on distributing the horizontal shear stress as the code seems unclear on this point.
Besides, is it OK for providing horizontal shear reinforcement in against the Utimate horontal force on the interface , regardness the horizontal shear stress distribution along the beam or slab?
If you know the answer then you should provide it rather than making smug comments.
If you don't then maybe you should go back to your books too.
My understanding of the question is the same as carlbauers
These forums are not for smart arses like Prex. to bolster their egos by sounding off to try to prove their superiority to themselves.
It's no wonder that the profession is in the state that it is.
Thank God that not everyone views learning in this manner. Hope that Prex never has to ask for help from anyone else.
Oswald19
missed out. I am also interested in this topic albeit for a
slightly different reason. What is the consideration required for
proper bond between old concrete (precast) and new concrete
(in-situ)? We recently designed a jetty with grid beams of such
composite construction. The lower half was precast, and the
upper half was cast in place. We computed shear stress at the
interface as per ( VQ/IB ) and provided shear reinforcement
and additional dowels to carry the horizontal shear. In such
cases we normally roughen the interface precast concrete
surface as early as possible after concrete sets, so as to acieve
better bonding with new concrete. I felt that
the reinforcement could be reduced, but could not confidently
justify it!
Incidentally, we saw the design of an adjacent jetty structure
designed by an australian firm. They had provided 225mm
thick precast concrete slab + 225 mm thick cast-in-situ
concreta slab. There were no dowels, stirrups etc. There were
no special notes. We were not confident about justifying the
composite action without being sure about the shear at the
interface. (We could not adopt that design concept anyway
because our loading cases were very different, and ours was
more severe).
Has anyone come across similar instances? This is a very
interesting and crucial situation. Significant reduction in
detailing and a greater confidence level in such construction
could be achieved.
Hariharan