Can anybody tell me, is it possible to use PPI Cable (I've got it from S7-200 starting kit) to communicate to S7-300 as well? Thanks.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: PPI-Cable for S7-300?
The S7-200 uses a PPI interface, the cable you have is for these units only. The S7-300 uses a MPI interface.
Both are RS485 based, but the protocols are different.
There are 3rd party interfaces available that will do both. I have not tested, but have heard reccommendations for the interface from Process-Informatik. It can detect the PLC S7-200 or 300 connected and changes protocol automatically.
http://www.process-informatik.de
Regards,
Darren.