BCT polarity testing

BCT polarity testing

BCT polarity testing

(OP)
A thread a while back strayed into the subject of testing BCT polarity while installed on a power transformer. I cannot find the thread anymore. Red flagged for some reason? Anyway, I mentioned performing such a test a few years back and claimed I didn't remember shorting the unused power transformer windings. I had occasion to do a similar test this past week, and the instructions were clear that the unused power transformer windings were to be shorted. The test set involved is a Multi-Amp ratio, excitation and polarity tester. I believe Multi-Amp is now Megger. The set applies a voltage to the CT secondary, and displays the primary voltage added to or subtracted from a fraction of the secondary voltage. When switched from add to subtract, reading will drop if polarity is correct and increase if reversed. We were able to quickly correct a REF protection scheme, and increase our confidence in a bus differential scheme.

Just wanted to clear up any misunderstanding I may have caused.

RE: BCT polarity testing

Hi Stevenal,

It was my thread - I think it is still there somewhere. Thanks for the update: I've got a generator transformer with a probable reversed neutral CT to test when it comes down for outage in the summer, and this method sounds considerably easier than a primary injection test. It's good to get some feedback from a user of the Megger unit rather than hearing the sales pitch.


-----------------------------------

Start each new day with a smile.

Get it over with.

RE: BCT polarity testing

Question: Is any industry standard in particular adhered to? Which one?

RE: BCT polarity testing

(OP)
Ralph.

Yes.

j,

C57.13.1 describes some of the tests this instrument performs, but this particular polarity test is not described.

RE: BCT polarity testing

Suggestion: Reference:
ANSI/IEEE Std C57.13-1978 An American National Standard IEEE Standard Requirements for Instrument Transformers,
Section 8.4 Polarity addresses three methods commonly used for determining CT polarity.

RE: BCT polarity testing

(OP)
8.4.3 is the basis of the method used.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources